10/06/2011 7:46 AM
what is the need of stabilized delta in Yy0 connection
Re: Yy0 With Stablized Delta
10/06/2011 2:04 PM
construct your one line diagram..
and post it here.. may be after that we may understand what are you trying to say?
Good Answers: 170
10/06/2011 10:12 PM
To provide a path for zero sequence currents
10/07/2011 2:56 AM
to supress the 3rd harmonic component of voltage in Tx.
Good Answers: 15
10/09/2011 9:35 AM
how does the third harmonic get suppressed in this case?
btw where did that third harmonic come from?
10/10/2011 5:28 AM
adding a 3rd delta winding to transformer, the 3rd harmonic component of voltage in delta will add up, causing a circulating current flow within the winding. This will supress the 3rd harmonic component of voltage.