Earth Fault and Differential Earth Fault

10/10/2011 12:40 AM

earth fault and differential earth fault both are same?

thanks for help

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: earth fault and differential earth fault

10/10/2011 3:25 AM

i have heard of 'Restricted Earth Fault' ..... i don't know if that is what you mean.

If so, look up this excellent answer :

http://cr4.globalspec.com/thread/44486#comment462746

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #1

Re: earth fault and differential earth fault

10/12/2011 10:43 AM

Restricted Earth fault relay is also known as "Ground Differential Relay" - particularly in IEEE.

Reply Score 2 for Off Topic
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#2

Re: earth fault and differential earth fault

10/10/2011 3:54 AM

difference is below

Earth Fault Rely (Restricted Earth Fault Now)

A Restricted Earth Fault (REF) means an earth fault from a restricted/localized zone of a circuit.REF protection is also applied to transformers in order to detect ground faults on a given winding much more sensitively than differential protection can do.

Differential Earth fault fault relay


Differential protection can also be used to protect the windings of a transformer by comparing the current in the power supply's neutral wire with the current in the phase wire: if the currents are equal then the differential protection relay will not operate; if there is a current imbalance then the differential protection relay operates

source:Internet

Reply
5
Anonymous Poster #2
#3

Re: earth fault and differential earth fault

10/10/2011 6:00 AM

Earth Fault is a fault when there is total or partial insulation failure causing large fault current to earth from the system which can cause total damage to system .also a insulation declivity caused by ageing of wiring or equipment insulations will cause a leakage current called earth leakage current,undetected by MCB or earth Fault relays but detected by ELR-CBCT (Sensitive Earth Fault Protection),ELCB etc .

there is no such thing as "Differential earth fault" but there is a "differential earth fault system" which is used to protect transformers, generators, etc against ground faults.

there are 3 kinds of differential earth fault system

1) restricted earth fault systems

2) partial differential earth fault system

3) modified differential earth fault system (percentage differential protection)

Restricted Earth Fault Protection is a type of zone of protection where Relay is connected in parallel with three phase CTs and one neutral CT. It will look just for faults inside the transformer, and need not to coordinate with relays downstream .the disadvantage is that it is affected by existence of an alternate ground path back to source

partial differential earth fault system is the one in which Differential relays sense the unbalance in the flow of currents in various apparatus or buses. In the absence of a fault in the protected zone, this unbalance tends to be small and the flows into the zone are closely matched to the flows leaving.This type of system is adversely affected by existence of an alternate ground path back to source. The current divides as a function of relative ground impedance parameters . Also It lacks sensitivity when used on a bus system where both buses are served by one source with the tie circuit breaker closed.

modified differential earth fault system (percentage differential protection) is the differential system arranged so that multiple source grounding doesnot affect system performance.

Reply Good Answer (Score 5)
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); kvsridhar (1); sriram1988 (1)

Previous in Forum: Electrical Design Software   Next in Forum: DC Voltage

Advertisement