Regarding Shorting Link in Busduct

10/14/2011 11:44 AM

Im working in Hydro Project in which we have used SPBD. We have used shorting link in phase side of Generator after CT, i want to ask that why it is required to use shorting link after CT. Cant we used this link before CT

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Regarding Shorting Link in Busduct

10/14/2011 7:01 PM

Shorting link is installed for providing the shorting facility of the CT secondary side before taking the CT load out from the CT circuit for any reason (maintenance or test etc.) while the system is energized. The shorting link is supposed to be installed in the CT secondary circuit before any load applied to the CT. I am not sure what do you mean by 'after CT' and 'before CT' here.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Member

Join Date: Oct 2011
Posts: 9
Good Answers: 3
#2

Re: Regarding Shorting Link in Busduct

10/16/2011 1:56 AM

As MSAMAD stated, all CT's need to have a shorting link on the secondary terminals. Once the CT secondary is connected to the burden devices (meters, relays, etc), the shorting links are removed. If the feeder circuit is energized with the CT secondaries open circuited, the voltage will go extremely high across the secondary terminals. An open CT secondary is an extremely hazardous condition; it can severly burn or even electrocute anyone who comes into contact, and it can damage the CT because the voltage rises much higher than the insulation rating of the CT secondary coil.