Multiplexer In PLC

10/14/2011 2:29 PM

hi everyone, in my plant we need to provide trip for the pump from the high value of bearing/winding temperature of motor. All interlocks are in plc and we also require indication in dcs. Earlier we required only indication in dcs but for safe engineering practise we are putting trip also. Now my problem is, i suggested usage of multiplexer for temperature signals but my senior told me that as interlocks are in plc so we have to use separate temperature transmitter for each temperature element (12 winding temperature element) , my question is, cant we use mux output to plc ?

__________________
I am man of simple taste.
Register to Reply
Pathfinder Tags: Multiplexer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Sep 2011
Posts: 11
#1

Re: Multiplexer In PLC

10/14/2011 3:16 PM

It is always advisable to use hard wire signals for safety systems.

Your senior has said it right....Trips and interlocks falls under IPS safeguarding system and it has its own criticality consideration on plant safety. Even you can go for voting systems in case if the trip is so crucial. I would advise to use a serial/modbus through multiplex for the indication to DCS.

The simple understanding of this concept is: Even if the multiplexed indication to the DCS fails, the pump would get tripped which is activated through hard wired signal to the PLC. So we ensure the safety requirement is given first preference.

You have to go through the Safety Instrumented system (SIS) philosophy studies and SIL studies to understand it to a larger extent.

Cheers.,

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#2

Re: Multiplexer In PLC

10/20/2011 9:12 AM

Multiplexing all temperature signals to the PLC would create a single point of failure in the interlock system: if the mux fails, the PLC loses ALL temperature indications, which might lead to a "fail dangerous" condition. Your senior has the right philosophy.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply