Neutral Disconnect Switch

10/28/2011 7:22 PM

Hi,

If a gen set is synchronized parallel with utility and its neutral switch fail to disconnect, what are the possible risk to the generator and the one who is operating it ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#1

Re: NEUTRAL DISCONNECT SWITCH

10/28/2011 7:35 PM

I'll go out on a limb here and say no real risk to anything. Where the gen connects to the utility the neutral should be connected to ground, so I can't imagine any problem if a switch does not disconnect the gen from the utility.

__________________
mike k
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: Neutral Disconnect Switch

10/30/2011 12:25 AM

I will go out on the limb, and say that it will blow up into your face.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Neutral Disconnect Switch

10/30/2011 1:04 AM

It is suggested to disconnect the neutral with the line conductors. In LRG (Low Resistance Grounding) or HRG (High Resistance Grounding) system, the neutral is not at ground potential. In the case of solidly grounded system, the neutral is supposed to be at ground potential but if neutral is not properly grounded, there might be voltage in the neutral. In all cases, there is possibility of having voltage at neutral point. So, if the generator neutral is not disconnected from the utility system (the utility neutral is connected to the generator neutral point), there is a risk of the presence of voltage at generator neutral and hence a risk of hazards to the generator as well as the operating and the maintenance personnel.

These related links also may help:

http://www.kraftpower.com/pdfs/KPC_Info_05_switching_neutral.pdf

http://www.cumminspower.com/www/literature/technicalpapers/PT-6005-GroundingAC-1-en.pdf

http://www.cumminspower.com/www/literature/technicalpapers/PT-6006-GroundingAC-2-en.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)