Surge Counter for Surge Arrester.

11/01/2011 2:44 AM

Hi

For a 2 MW - three phase hydrogenerator in a powerhouse, surge arresters is kept. The number of surge arrester required will be three, and number of surge counter required will be one??

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#1

Re: Surge Counter for Surge Arrester.

11/01/2011 5:13 AM

you need three surge counter ie one for each phase.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2
In reply to #1

Re: Surge Counter for Surge Arrester.

11/02/2011 2:08 AM

Will it be acceptable if all three outgoing leads from surge divertors are connected together and passed through the counter?.

__________________
pnaban
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#3
In reply to #2

Re: Surge Counter for Surge Arrester.

11/02/2011 4:37 AM

that is what is mentioned in a manual...........that connected together and passed through the counter...........!! We are talking about 6.6 kV systems here.

regards,

sks

Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#4

Re: Surge Counter for Surge Arrester.

11/02/2011 5:51 AM

Yes ,you can do that but it will the sum of fault on three phases.If you have three counter you can measure the fault on each phase ,which may help to find the frequent faulty phase and to take corrective action.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#5
In reply to #4

Re: Surge Counter for Surge Arrester.

11/02/2011 6:11 AM

thanks sri ram for answer.

sks