We have installed Allen Bradley power monitor PM3000 with input voltage of 3.3KV and configured with 2PT's and 3 CT's and the following parameters are only shown:
  1. 1. L1 and L3 = 3.3KV
  2. 2. L2 = 0 KV
We try several choices/setting below with negative result:
Your choices include the following:
  • • Delta 3 CT
  • • Delta 2 CT
  • • Direct Delta 3 CT
  • • Direct Delta 2 CT
  • • Open Delta 3 CT
  • • Open Delta 2 CT
  • • Wye
Need your feedback on how we can configure and achieved our objective to display all the parameters(L1,L2,L3, KW-hours etc.)
See attach wiring diagram:
Thanks in advance for your feedback -Nelson
nlp
Pathfinder Tags: power monitor Rockwell/AB
Good Answers: 131
Re: Rockwell/AB - Power Monitor PM3000
11/02/2011 9:46 AM
By the schematic & wiring diagram you provided, you should choose Open Delta 3 CTs. The PTs are configured in an "open delta" arrangement, with windings forming two sides of a 3-phase delta transformer circuit. Check your wiring carefully - your snapshot of the diagram is rather small and fuzzy, so I cannot make out all the connections, but if it doesn't work you may have something wired wrong.
Good Answers: 804
11/02/2011 10:37 AM
If you are reading 0 volts on L2, the configuration of your CTs (CURRENT Transformers) has absolutely nothing to do with that. You have made a mistake on the wiring of your PTs (POTENTIAL Transformers, as in Voltage Potential) .