Tripping of Relay

11/04/2011 11:20 AM

How to overcome the nuisance tripping of relays for protection of 33KV/11KV, 7.5MVA transformer during synchronisation of 2000HP auto synchronous induction motor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Tripping of relay

11/04/2011 11:29 AM

You should first ask yourself this question. Which is the bigger nuisance, resetting a protection relay or blowing up what the relay tried to protect?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Tripping of Relay

11/04/2011 5:55 PM

What indication is the relay giving when it trips.

You should be looking for a "real" fault, not trying to mask it by changes to the relay settings. I hope the system was set up by an engineer of some repute.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster #1
#3

Re: Tripping of Relay

11/05/2011 1:28 AM

2000HP = almost 1500KW =1.5MW which may be about 1800MVA at input (electrical)

The starting current in case yiou are DOL starter may be about 5-6 times minimum and that corresponds to the current of 9MVA (though I don't expect that you might be doing such a large motor on DOL)

Register to Reply Off Topic (Score 3)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Tripping of Relay

11/06/2011 9:02 AM

If you feel tripping is nuisance, why have a relay at all? Throw out the relay and... start stocking enough transformers.

Register to Reply