Separate CT Core for Generator Differential Protection?

11/09/2011 1:10 PM

Is it necessary for the differential protection system, especially of a generator, to have a pair of dedicated CT cores? Is it possible to share CT output from a CT core for the differential protection? I'm guessing otherwise. Anyways, please help remove my doubt with some solid reasons!

__________________
leokhk@yahoo.com
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Separate CT Core for Generator Differential Protection?

11/09/2011 10:24 PM

The question is not clear to me. However, it appears you do not want to use dedicated CT pair for differential protection, rather want to use same CT for other protections such as short circuit protection etc. You cannot do this because

(1) For differential protection, the burden for both side CTs should be same. If you add other protection relay to the one side CT, there will be load imbalance and it will initiate false trip signal.

(2) Differential protection requires special type of CT, not the regular protection CT.

Hope it was helpful.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2010
Posts: 10
#2
In reply to #1

Re: Separate CT Core for Generator Differential Protection?

11/10/2011 1:20 AM

Thanks! One more question, though. Does the CT secondary current for both the CTs in the pair also need to be equal. For instance, for transformer differential protection, is it possible to use a CT at the LV side with secondary current 5A while using CT at HV side of secondary current 1A?

__________________
leokhk@yahoo.com
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Separate CT Core for Generator Differential Protection?

11/10/2011 3:47 AM

Nope! IOf so, even during healthy conditions, assume taht the transforemr is fully loaded, the LV CT will feed in 5A and the HV CT will feed in 1A; then there would be differential current and the relay would trip for sure. If unavoidable, you can use an interposing CT to match the current at the relay point.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4
In reply to #3

Re: Separate CT Core for Generator Differential Protection?

11/10/2011 5:17 AM

I hope we should think the ans w.r.t todays advanced digital relay. It will see the magnitude. The CT secondary current is converted to voltage of very low magnitude to operate relay. In a broad sense old concept of Diff CT philosophy is now a days is very much modified. Please see manual of relay manufacturer.

__________________
BNDas
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

biswanath.das (1); electricalexpert65 (1); Leo342 (1); msamad (1)