Grounding Generators Connected to a Bus at Generator Voltage

11/12/2011 10:31 AM

I've seen examples of generators connected to a bus at the generator voltage having grounding system in which only one generator is connected to ground at a given time. Can somebody explain if it is a correct practice?

__________________
leokhk@yahoo.com
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Grounding generators connected to a bus at generator voltage

11/12/2011 11:15 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#2
In reply to #1

Re: Grounding generators connected to a bus at generator voltage

11/13/2011 12:51 AM

Thanks! I should probably search the web and this forum before i post a question. However, one question still remains. What if there is a stator earth fault at one of the generators not connected to the neutral?

__________________
leokhk@yahoo.com
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Grounding generators connected to a bus at generator voltage

11/13/2011 1:28 AM

Then, the earthed generator would feed into the stator earth fault in the unearthed generator. Now, in the unearthed generator, its REF Relay would trip, as its phase CTs would only sense the fault current and not its neutral Ct. Incidentally, I have recently sent a detailed write-up on tis issue to some other forum members, who were also having similar doubts. Pl. inform me your mail ID thro this forum's mailbox, so that I can send you the same.

Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2011
Location: Qatar
Posts: 8
#4
In reply to #3

Re: Grounding generators connected to a bus at generator voltage

11/13/2011 4:55 AM

But then how the REF Relay would be connected in the un-earthed Genset if its Neutral is not earthed?

Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 10
#6
In reply to #3

Re: Grounding generators connected to a bus at generator voltage

11/14/2011 11:05 AM

Wow, thanks! Would a differential generator protection(87G) work as well as a REF (64R)? If so, under what condition would each be suited for protecting the generator?

__________________
leokhk@yahoo.com
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #6

Re: Grounding generators connected to a bus at generator voltage

11/14/2011 8:41 PM

Why should you worry about differential protection? Your question revolves around grounding of the neutral and as such your concern should be more on ground fault protection which my paper sent to you would have clearly answered. As regards differential, it does not matter whether the generator neutral is grounded or not. It would operate mainly for phase faults.

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#5

Re: Grounding Generators Connected to a Bus at Generator Voltage

11/13/2011 5:46 AM

The practice of grounding only one generator at a time is good for isolated running plants which are not connected to grid.

But in case of plant connected to grid, then all generators neutrals should be grounded unless and until

1. you have a generating transformer between utility bus and plant bus.

2. gen manufacturer gen damage curve is above the the third harmonic current curve.

Register to Reply
Register to Reply 7 comments