I've seen examples of generators connected to a bus at the generator voltage having grounding system in which only one generator is connected to ground at a given time. Can somebody explain if it is a correct practice?
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Re: Grounding generators connected to a bus at generator voltage
11/13/2011 12:51 AM
Thanks! I should probably search the web and this forum before i post a question. However, one question still remains. What if there is a stator earth fault at one of the generators not connected to the neutral?
Re: Grounding generators connected to a bus at generator voltage
11/13/2011 1:28 AM
Then, the earthed generator would feed into the stator earth fault in the unearthed generator. Now, in the unearthed generator, its REF Relay would trip, as its phase CTs would only sense the fault current and not its neutral Ct. Incidentally, I have recently sent a detailed write-up on tis issue to some other forum members, who were also having similar doubts. Pl. inform me your mail ID thro this forum's mailbox, so that I can send you the same.
Re: Grounding generators connected to a bus at generator voltage
11/14/2011 11:05 AM
Wow, thanks! Would a differential generator protection(87G) work as well as a REF (64R)? If so, under what condition would each be suited for protecting the generator?
Re: Grounding generators connected to a bus at generator voltage
11/14/2011 8:41 PM
Why should you worry about differential protection? Your question revolves around grounding of the neutral and as such your concern should be more on ground fault protection which my paper sent to you would have clearly answered. As regards differential, it does not matter whether the generator neutral is grounded or not. It would operate mainly for phase faults.