NGR Question

11/14/2011 8:35 AM

Hello all,

Can you please provide sizing calculation for NGR for following data

System Voltage : 11kV

Transformer Rating : 11/0.415kV, 2.5MVA, 6.25 %Z

Calculated LV side Fault Current : 55 KA

LV side switchgear is rated for 50kA/3sec. But the calculated LV fault current is 55kA. So, it is necessary to reduce the fault current by using NGR. Can you please provide guidance to size the NGR.

Best Regards,

Bhuvan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: NGR Question

11/14/2011 10:10 AM

Do you use the neutral in your system? If you do you should not use a NGR

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: NGR Question

11/14/2011 10:37 AM

NGR Ohmic Value = System Phase Voltage / Desired Earth fault current. In your case, the System Phase Voltage for the LV side would be 240V. The desired earth fault current is (assumed to be) the short time withstand rating of the LV bus (i.e.) 50kA in your case. Hence, the NGR sizing shall be: 240 / 50000 = 4.8 milliOhms. And, the voltage rating of the NGR shall be 240V. But, I feel that for a ground fault in the bus bars, the bus bar impedance itself would be much more than 4.8 milli-ohms to limit the earth fault current to 50kA. So, you need not go for any external NGR for limiting the fault current from 55kA to 50kA. Pl. remember 55kA fault current is arrived by considering only the transformer impedance.

Moreover, here in India, one is not permitted by Law to go for any other method of earthing than Solid Earthing for the LV side. Pl. check what is the law in your country of operation.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: NGR Question

11/14/2011 10:42 AM

Pl. see revised posting above.

Register to Reply
Register to Reply 3 comments

Previous in Forum: Zero Crossing Detector at 230 V AC Mains   Next in Forum: Working in Under Voltage

Advertisement