Creepage Distance

11/16/2011 11:43 AM

Basically creepage distance is the distance over which the charge flash over or starts conducting. Generally in a normal atmospheric conditions it was considered as 16mm/KV and for polluted conditions it will be considered as 31mm/KV. Whether this creepage distance will be used for calculating the distance between the conductors and the ground. If so on what basis it will calculated.

If clearance = Voltage level X creepage distance, then for 110KV level it would be 1760mm. But in the substations of 110KV level, i found the distance is around 1.1 to 1.2meters only. Is this correct or wrong.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: creepage distance

11/16/2011 11:52 AM

Creepage distance is along the surface of the insulator, not line-of-sight from the energized part to ground. That is why the insulators or bushings are ribbed. The creepage is along the long, convoluted path, and has a much farther distance to travel to get to ground. In addition, the ribs or "skirts" shed water off their edges, breaking up the conductive path that water flowing down the insulator would create in wet or rainy conditions.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Anonymous Poster #1
#2

Re: creepage distance

11/16/2011 11:53 AM

Creepage distance is the shortest length between two conductors along insulating surfaces.

Clearance distance is the shortest length between two conducting media. (almost always through air)

Air breakdown voltage is a few million volts per meter.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: Creepage Distance

11/16/2011 1:04 PM

Creepage seems like a pseudo science to me since it dosen't take into account what kind of junk accumulates on said surface, or the specific environment. It implies that not all insulators are perfect and sometimes those insulators can become contaminated with conductive materials. Perhaps there is a better definition somewhere but I don't see how anyone could apply a specific formula without indicating some sort of environmental conditions at the same time.

Creepage is used in determining the "proper" distance between connected pins and the base metal in the endcap of a fluorescent lamp. It is also used on ceramic insulators on high voltage equipment. Surely there are significant differences that makes this apples and oranges.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Creepage Distance

11/16/2011 3:04 PM

NYOJ,

Contamination is addressed in creepgae distance (although the OP had it BACKWARDS in is original statement). "Creepage distance" is the term used for IEC standards, in North America where we use ANSI, the term is "leakage distance", at least when referring to MV and HV insulators and bushings.

IEC 60815 (and others, depending on the equipment involved, but they are all the same I think):

Table I: Contamination level in relation to a description of the pollution in some typical environments.
I = light
II = medium
III = heavy
IV = very heavy

I couldn't find a specific PD reference for 60815, but this is from another IEC standard, they are essentially the same.

  • Pollution degree I. No pollution or only dry, nonconductive pollution occurs. The pollution has no influence.
  • Pollution degree II. Normally only nonconductive pollution occurs. Occasionally a temporary conductivity caused by condensation must be expected (example: product used in switchgear in a normally clean dry environment).
  • Pollution degree III. Conductive pollution occurs, or dry, nonconductive pollution occurs that becomes conductive due to expected condensation (example: products used in heavy industrial environments that are typically exposed to pollution such as dust).
  • Pollution degree IV. Pollution generates persistent conductivity caused, for instance, by conductive dust or by rain or snow.

Table II: Minimum creepage distance for each pollution level :
Level I : 16 mm/kV of highest system voltage phase to phase
Level II : 20 mm/kV
Level III : 25 mm/kV
Level IV : 31 mm/kV

For us in North America, the standard is ANSI/IEEE C57.19.100

Contamination

Voltage: L-G
Light 28 mm/kV
Medium 35 mm/kV
Heavy 44 mm/kV
Extra Heavy 54 mm/kV

Voltage: L-L
Light 16 mm/kV
Medium 20 mm/kV
Heavy 25 mm/kV
Extra Heavy 31 mm/kV

Notice they are the same. Wonders never cease...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5

Re: Creepage Distance

11/16/2011 5:23 PM

I thought creepage distance was how far they had to stay away from a school or a playground...................

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Off Topic (Score 5)
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (1); KJK/USA (1); NotUrOrdinaryJoe (1); PeterT (1)

Previous in Forum: S3WR power transducer   Next in Forum: About Pilc Cable and Xlpe Cable

Advertisement