Previous in Forum: Underwater Shaft Seals   Next in Forum: Rotor Shaft Defective
Branch Connection Reinforced Pad Calculation
12/03/2011 11:36 AM
Hi,
I am fairly new with this calculation.
This is 18 x 18 at 45° wye lateral.
Dh = 18 in, Th= 0.562 in
Db = 18 in, Db = 0.562 in
Design pressure 550 psi, corrosion = 0.1, Design Temp = 160° F
Material = A106-B, Allowable = 19,000 psi.
Calculated Result for Design thickness of the pad.
th = 0.258 in, tb = 0.258 in
When I model this Wye Lateral using FEA.
I need to use at least 1" thick material to meet the allowable of 19000 psi.
Re: Branch Connection Reinforced Pad Calculation
12/03/2011 4:29 PM
What is your application that requires 19000 psi ??
Anonymous Poster #2
12/03/2011 7:46 PM
The allowable should be 20,000 psi for B31.3 from Table A-1.