ETAP Clarification

12/06/2011 2:13 AM

Dear friends,

The drawing shown is the proposed SLD for my project. Our subcontractor is doing ETAP calculation. In that calculation he considered one common bus without any coupler and done the Load flow study. The main point is both transformers are running. He is saying that I have considered infinite bus so only not considered bus coupler. The infinite bus shall have constant voltage and frequency only. but the incoming cable size has been sized for inidividual Transformer load. but he clubed the two transformer in single bus. please clarify this study is correct or not? His report model is also attached in reference..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: ETAP CLARIFICATION

12/06/2011 6:28 AM

Not a good idea i think. Too much dependance on unrealistic theory. After all, there isn't an "Infinity" that you can lay your hands on is there? Two transformers will never be identical, and circulating currents will be unavoidable i feel. Not my field, just my humble opinion. One bus coupler is desirable.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 21
#2
In reply to #1

Re: ETAP CLARIFICATION

12/06/2011 8:14 AM

thanks for your reply.. could you please give me valuable reason to argue with that people.. because as for my exp its compulsory of bus coupler..

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: ETAP CLARIFICATION

12/06/2011 8:53 AM

Circulting currents, due to some small differences somewhere. Agreed that paralleling of sources is meticulously done, but in the event that these circulating currents do occur, you have the bus coupler which can be switched off.

Not my field really, let us hope you will get some better answers.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Sep 2011
Posts: 5
#4

Re: ETAP Clarification

12/07/2011 12:26 AM

Hi,

If the transformer primary is a utility source(Electricity board substation) and you are assuming that is a infinite then considering the utility bus as a single bus (without bus tie) is acceptable.

If transformer primary feeder protective device (breaker)is in your scope of work, you need to model it seperately.

Regards,

Mari

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 21
#5
In reply to #4

Re: ETAP Clarification

12/07/2011 12:49 AM

The transformer primary is fed from VCB of 34.5kV intermediate switchgear. The supply for this intermediate Switchgear is from Ring Type distribution system in Switching station. From this switchgear Two seperate feeders also shall run to another plant.

Register to Reply
Member

Join Date: Sep 2011
Posts: 5
#6
In reply to #5

Re: ETAP Clarification

12/07/2011 1:14 AM

Since, 34.5kV intermediate switchgear is feeding another plant, i beleive 34.5kV intermediate switchgear is owned by utility company(Electricity board).

If you know the maximum short circuit available in each bus need to model the 34.5kV Bus A and B seperately run the study with various scenario.

If you are assuming the short circuit contribution (as infinite source), study result shall not vary even if you considered a single 34.5kV bus instead of Bus A & B.

Apart from the above technical points you can insist the power system study vendor to model the system as per the actual condition so that anybody can understand the system easily in the future.

Regards,

Mari

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 21
#7
In reply to #6

Re: ETAP Clarification

12/07/2011 1:51 AM

Thanks a lot Mr, Mariappan, This intermediate switchgear shall be owned by client only not by electricity board. i already told vendor to do as per requirement. But he is not accepting that. Thats why I am asking to expert people for better idea..

Thing is The transformer is not directly fed by source, the source power shall come intermediate swgr first. From that swgr there are four outgoings. So only I am not accepting the single source like you..

Let me talk with him once again and see the result.

Once again thanks Mr. Mariappan..

Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 13
#8

Re: ETAP Clarification

12/07/2011 10:13 PM

There is nothing to say he has paralleled the transformers, they are just connected to the same source which 99% of transformers in the world are. If you cannot understand the model pay someone to review it rather then get "expert" comments from internet.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: ETAP Clarification

12/07/2011 10:22 PM

Er.....i do believe that BOTH the primaries and secondaries are connected together....the primaries to the infinite source, and the secondaries to the load's busbar. This used to be called 'paralleling' when i studied way back in 1965. Maybe things are different now?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 13
#10
In reply to #9

Re: ETAP Clarification

12/07/2011 10:30 PM

Well you're drawing and words do not show that but you obviously have a lot of experience hence seeking advice. By the way who is getting paid to review contractors work, what is your role?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: ETAP Clarification

12/07/2011 10:54 PM

My friend, you should learn to read before writing.

1. i am NOT the Original Poster. The OP is rathakrishnan05. OK?

2. i am NOT seeking any advice. i am trying to give one opinion.

3. None of your business what my role is. Or who is getting paid. And how much. You have just started in CR4. Better learn some etiquette.

4. The diagram given by the OP shows the secondaries of the transformers connected to one bus. It is a logical assumption that the primaries are connected to the Utility. So they are paralleled. QED.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 21
#12
In reply to #8

Re: ETAP Clarification

12/08/2011 6:18 AM

Mr.dbman kindly note nobody born in geneious in this world. people become genious by correcting their mistakes in past exp. If you can answer but dont discourage by using these type of words.. anyway thanks for your comment also...

Register to Reply
Register to Reply 12 comments
Copy to Clipboard

Users who posted comments:

dbman (2); kvsridhar (4); Mariappan (2); rathakrishnan05 (4)

Previous in Forum: Transformer   Next in Forum: Fuzzy Logic Controller

Advertisement