Dear learned gentlemen, and others,
query about odd test results. The installation is a 50KVA 3 phase DG feeding a distribution board which is the MEN point. From the DB feeds run out 150 to 200 metres to 5 different sub boards by way of 3 core and earth (no neutral), and the sub boards then feed motor control cabinets. A second earth stake exists at the motor. When testing earth continuity with all earths connected, and breakers off, we found 11 ohms resistance. When isolating the respective earth from the earth bar in the DB we found only 4 ohms resistance. The resistance of the trailing lead is 3.8 ohms. Of course the DG is off during testing so no real voltage to speak of and continuity testing was done with a mutlimeter.
I'd like to better understand what was happening when testing with the earth cable connected. We assumed (?!) that taking the least path of resistance would provide accurate results.