Sinking Digital Input Module

12/31/2011 8:23 AM

We have a plc with sinking type input module means N24 or 0 is distributed in field. What happens if this N24 opens and connectsto ground or earth????

__________________
pstanwar9229
Register to Reply
Pathfinder Tags: negative ground sinking
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: sinking digital input module

12/31/2011 8:36 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
2
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#2

Re: Sinking Digital Input Module

12/31/2011 10:57 AM

A "sinking" input module sinks current to ground, which means the 0 or N24 power supply terminal connects to the "Common" terminal on the module, and the P24 or (+) terminal of the power supply is distributed in the field.

To see an example of this, download this Allen-Bradley PLC I/O module manual and look at the example wiring for the 1756-IB16 sinking input module on page 146:

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um058_-en-p.pdf

As you can see, the (-) side of the power supply connects to the "GND" terminals on the module, while the (+) of the power supply goes to the common sides of the field switches.

If your field switches have N24 (-) distributed to them, then the module you need in your PLC is a "sourcing" module where the common terminal(s) on the module connect to the P24 (+) terminal of the DC power supply. An example of this for you to see is the Allen-Bradley 1756-IV16 sourcing DC input module on page 173 of the same document.

In answer to your general question of what happens if one of the power supply bus wires opens and the field wiring goes to earth ground, that all depends on how solidly one of the power supply's terminals has been grounded itself. In most cases, the PLC will fail to receive a signal from the field device if this happens, but the details of your particular installation are what matter to you.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply Good Answer (Score 2)
Active Contributor
India - Member - New Member

Join Date: Oct 2010
Location: India
Posts: 20
#3

Re: Sinking Digital Input Module

01/03/2012 3:46 AM

I am talking about input module in which n24 spread in the field like push button, limit switch etc. And this n24 comes back to DI module where n24 is common supply. We hv QX42 input module. My question is that if n24 cable went to field would get shortd with earth then how would we know if our wire get shorted as we continue get ground or 0v or n24 from field.

__________________
pstanwar9229
Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

pstanwar9229 (1); SolarEagle (1); tonykuphaldt (1)

Previous in Forum: How Do I Use Osciloscope to Detect Fault in Electronics   Next in Forum: What Is the Reason for Tapering the Tube of Rotameter?

Advertisement