Ice Cube Relay

01/03/2012 3:11 PM

I am trying to figure out how to make this work. I have a Toshiba H9 ASD that is replacing an older H3. I have an E-Stop in a remote location that has always been used to shut off the drive, but with the new drive, once the E-Stop is pulled, the drive will start running again. The E-Stop is running off a N/O contact. I need to wire another relay for a reset so that once the E-stop is pushed, the drive cannot start until the reset has been pushed.

Thanks for the help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#1

Re: Ice Cube Relay

01/03/2012 3:54 PM

If your relay has an additional set of contacts, use the spare N/O contact to latch your relay coil. You will need a N/C momentary switch in series with the contact to reset the relay.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Ice Cube Relay

01/03/2012 3:58 PM

I don't see the problem here...Is the question about the particular relay to use?

Relay with manual reset

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: Ice Cube Relay

01/03/2012 4:46 PM

The H9 has inputs for forward and reverse command inputs from a switch. There is selection with in the programing to select a remote command. Along with that E stop is there a start button?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Participant

Join Date: Jan 2012
Posts: 2
#5
In reply to #3

Re: Ice Cube Relay

01/04/2012 6:42 AM

The Forward is where it gets the run command. It is powered from the E-stop relay. It is started from the Run button on the display. I can do a start/stop from our PLC, but we still have the safety issue problem with the drive running as soon as the Press operator, who is in a different building, pulls the E-stop. If there is no one in the control room, where the drive is located, to stop the drive then we have the possibility of the tank over flowing.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#6
In reply to #5

Re: Ice Cube Relay

01/04/2012 6:59 AM

I am with Ozzb on this one. You should be able to find the correct "E-Stop" circuit in the manual for the unit. It sounds like terminology is off a bit on what your calling a stop button and what an "E-Stop" is. If it is wired as stated, it is a stop button only and the unit will start as you suggest. If you do not have a controls person in your group, ask the supplier to give you some technical help on this one. It is hard for any of us to determine a fix without seeing all of the information. Most of these types of controllers are very versatile and can be made to have controls as needed without adding relays.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#7
In reply to #5

Re: Ice Cube Relay

01/04/2012 7:05 AM

The E-stop should cut all source of power to control circuits. It should not be applying power as a signal to the forward command terminal when engaged. This input is momentary. Place the E stop in the circuit so it cuts all control power. Then you will have to press the run button to get it started again.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Ice Cube Relay

01/04/2012 3:26 AM

Your E stop should be n/c in the latching circuit with manual latch reset.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#8

Re: Ice Cube Relay

01/04/2012 11:09 AM

It sounds as if the new drive may be configured for 2 wire control, and the old drive was 3 wire control. Check your drive parameters.

If this is an E-Stop, it should be wired in the E-Stop circuit, not the start stop start circuit. Check your wiring.

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#9
In reply to #8

Re: Ice Cube Relay

01/04/2012 1:38 PM

I agree, or use it in the "Enable" I/O input whatever the Mfg. or situation allows.

__________________
It's not Rocket Science
Register to Reply
Power-User

Join Date: Jul 2007
Location: Melbourne Florida
Posts: 122
Good Answers: 2
#10

Re: Ice Cube Relay

01/04/2012 4:05 PM

Since the OLD drive operated they way in which you intended, then check your control parameters. Make sure that auto restart is OFF. Also Make sure that the wiring is correct. Is the E Stop between the CC and ST terminals? Is the Run command dropping out when the E-Stop is pushed?

On The H9 drive you can monitor the input to verify what commands you are giving the drive. ( see the manual )

__________________
repeat problems can not be solved by the same way of thinking ( A. Einstein)