Loads for Unit Auxiliary Transformer

01/06/2012 3:54 AM

hi,

I have read that loads for unit auxiliary transformer in a hydro-plant is connected to 400 volt supply systems for auxiliary load. And the load basically consists of motor loads of 400 volts - for station service system delta connected ungrounded system is used.

Why is this preference for delta connected ungrounded system ?? Whereas in case of commercial or industrial loads, it is predominantly lighting load - and 400 V star grounded system is used.

Explanation is expected.

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: loads for unit auxiliary transformer.

01/06/2012 5:36 AM

sauravbabu, you will find you get a rather better response to your queries in this (and I suggest any other) forum if you learn to phrase things better.

The statement "Explanation is expected" is demanding and impolite. I future, try something like "Can anyone please explain?".

No-one here gets paid to sit waiting to dish up your "expected explanations".

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Loads for Unit Auxiliary Transformer

01/06/2012 9:07 AM

Explanation may be expected, but with an attitude like that I doubt you'll get one.

It's about time you did some of your own work.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Loads for Unit Auxiliary Transformer

01/06/2012 10:55 AM

I agree completely with JohnDG and TonyS, you need to learn how to pose questions without getting people teed off.

Having said that...

This topic has come up many times during discussion with various trades people and it is surprising the number that do not know why such a system would have been specified.

The answer is simple... reliability. In an ungrounded delta system, when you loose a phase via a short to ground, there is no impact on the system. Because there is no path back to the faulted source there is no where for fault current to flow to. Things will continue to work. Which is why they are often times specified for systems with high up time needs.

The down sides... you need special ground indication equipment to know when a phase has in fact gone to ground. You need electrical maintenance resources to track down the grounded conductors. And perhaps most of all... when a second failure happens, it is at full phase to phase potential and not phase to neutral so the fault current is greater.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#4
In reply to #3

Re: Loads for Unit Auxiliary Transformer

01/08/2012 3:53 AM

I could not understand properly.......!!

"The down sides... you need special ground indication equipment to know when a phase has in fact gone to ground." (You mean in ungrounded delta? or a ground relay can serve the purpose?)

"You need electrical maintenance resources to track down the grounded conductors. And perhaps most of all... when a second failure happens, it is at full phase to phase potential and not phase to neutral so the fault current is greater." (This is with ungrounded delta?)

- Again, in industrial loads with major of lighting loads - why grounded star to be used - why not ungrounded delta for reliability ? (Because lighting loads require neutral point?)

Regards,

sks

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #4

Re: Loads for Unit Auxiliary Transformer

01/10/2012 9:25 AM

You said... "The down sides... you need special ground indication equipment to know when a phase has in fact gone to ground." (You mean in ungrounded delta? or a ground relay can serve the purpose?)

Yes... the ground fault indicator serves to show when one of the phases has shorted to ground. As to a "ground relay", that means nothing to me. You need a ground fault indicator designed for ungrounded systems.

You also said... "You need electrical maintenance resources to track down the grounded conductors. And perhaps most of all... when a second failure happens, it is at full phase to phase potential and not phase to neutral so the fault current is greater." (This is with ungrounded delta?)"

When you loose a phase to ground on a ungrounded system, you must isolate the fault and repair it as soon as possible because of the danger involved in a full phase to phase fault occuring.

You also said... "- Again, in industrial loads with major of lighting loads - why grounded star to be used - why not ungrounded delta for reliability ? (Because lighting loads require neutral point?)".

Lighting loads do not require a neutral point. The benefit of using a grounded system is the reduction in fault current levels.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Loads for Unit Auxiliary Transformer

01/09/2012 7:46 AM

Oh! Yet again!

In electrical rotating machines, any earth fault would definitely involve the core. And, the core laminations have a very limited I2t capacity. Manufacturers generally give this as core damage curve. If you earth your system supplying rotating electrical machines by solid earthing or low resistance earthing or reactance earthing, the earth fault current would be much more than the tolerable levels of the rotating electrical machines connected to the system. And, core damage is sure to happen. Winding damages in rotating machine scould easily be rectified with local rewinders. But, for rectification of core damage, the machine has to be sent back to the manufacturer; thus causing an unacceptable reapir time and plant downtime. In case of unearthed system or a high-resistance earthed system, the earth fault current is kept to a value less than the core damage current levels. Thats why in systems supplying rotating electrical machines, it is preferable to have a high resistance earthed system or better still, an unearthed system, wherein the current is kept below the core damage levels, even in the case of an earth fault in the system. But, it might be difficult to identify or locate the first fault.

Then why in other commercial and industrial (lighting loads), the system is solidly earthed? Good question! You see! In commercial and lighting installations, it would be the common public (non-technical) who could handle electicity. Here, in the event of an earth fault, if isolation is not guaranteed within a very quick time, the person could get hurt, fatally too! Only in solidly earthed systems, as the earth fault current is equal to the three phase fault current, definite isolation is guaranteed, in the event of an earth fault, even with any short circuit protective device like a fuse, without any need to go for any special earth fault protective device such as ELCBs. Of course, chances of core damage in rotating electrical machines, present in such systems, is more, but, then, human life is always more precious than a core life, you know!

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: