LV Cables Fault Location

01/08/2012 3:14 PM

Dear Members

Please suggest the best and cheap solution for locating fault in LV 4 Cores 185mm2 XLPE/PVC Cables. All Phase to Phase Insulation resistance is good but One Phase to Ground Insulation is Zero, means this phase insulation is damaged and conductor touching ground, The cables are layed on Ground one meter deep.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: LV Cables fault Location

01/08/2012 3:41 PM

You might try this...

http://www.abb.com/cawp/seitp202/003a314df08e8aedc12578380056f1f3.aspx

....or Buy this setup, looks expensive, and learn how to use it..

http://www.tek.com/application/time-domain-reflectometry-tdr

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: LV Cables fault Location

01/08/2012 3:56 PM

You want the best and the cheapest solution to your problem. Have you ever heard the phrase, "You get what you paid for." Cheap is rarely the best solution and it is often the most expensive solution.

I did a brief search of XLPE/PVC cable types and none of the cables I found were rated for direct burial. So your one meter deep cables should be inside conduit of one type or another. So once your well paid, high skilled electrician/technician determines which cable has the short, this damaged cable can be used as a pull rope to replace the damaged cable with a new undamaged cable.

Now how your well paid electrician/technician will determine which cable has failed will change significantly depending on unstated conditions of your installation. The first thing I'd try is identifying the actual impedance of your short, it is not zero ohms. Your cable is not a super conductor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: LV Cables fault Location

01/08/2012 4:11 PM

Wait until dark, crank the power up to max and look for the glow.

Alternatively, pour salt water on the ground to saturate the wire run and, using a proper sensor (such as your tongue) search for the leak. This test can be performed at any time, day or night.

Hope this helps.

OK, this is a joke.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: LV Cables fault Location

01/08/2012 5:03 PM

This guy might do it...cheap

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#6
In reply to #4

Re: LV Cables fault Location

01/08/2012 5:55 PM

THAT AIN'T NO GUY - SHE looks familiar, I got really, really drunk once and.........................Oh forget it

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #4

Re: LV Cables fault Location

01/08/2012 7:31 PM

We have a saying in Arizona. Coyote Ugly!

Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#14
In reply to #4

Re: LV Cables fault Location

01/09/2012 10:37 AM

I bet he will..he will have to go by boat, they won't let it on an airline.

__________________
It's not Rocket Science
Register to Reply Off Topic (Score 5)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5

Re: LV Cables fault Location

01/08/2012 5:09 PM

Based on your initial comments - you are correct, zero means conductor insulation is faulted.

Isolate fault between point A and B perhaps between manholes or J-B's.

Pull faulty cable back with a pull line.

Pull in new conductors using pull line (that you attached to the faulty cable when you pulled it out), use lube, pull, trim, terminate, megger, and walk away.

There is no "cheap" solution, only the "correct" solution.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#8
In reply to #5

Re: LV Cables fault Location

01/08/2012 11:43 PM

Pull in ground buried cable?

__________________
Plenty of room here
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#12
In reply to #8

Re: LV Cables fault Location

01/09/2012 8:27 AM

Your right, I should have read the post all the way through

I ASSumed buried in conduit.

Either way, if he could isolate the fault (won't be easy) he could replace the faulted section.

Raychem sells some great direct burial splice kits.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: LV Cables Fault Location

01/09/2012 6:48 AM

May be a water-diviner...?

Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 24
#10

Re: LV Cables Fault Location

01/09/2012 7:31 AM

Go to an electrical wholesaler and ask for a cable fault locator and they will advise you.

Another option is to approach an electrical services company in your area and they will do the job for you, that is a big cable .

JS

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11

Re: LV Cables Fault Location

01/09/2012 8:24 AM

A TDR (time domain reflectometer) of some type is the instrument that will locate an impedance discontinuity in a transmission line and report the distance to fault. Solar Eagle also recommended this. Not so expensive but definitely not cheap (unless you can get to use one for mate's rates)

Now, before buying, renting or borrowing this instrument, conducting an investigation, scoping out a solution and mobilising a repair crew you want to be sure you really have a problem.

Are you sure it is a phase to ground fault and not a phase to neutral "fault"? Check if anybody has tapped into the energy path on the cable side of the isolation devices. Perhaps someone has "temporarily" connected a work lamp (airconditioner, whole household, small factory...) onto one phase of the cable/busbar in a transformer cabin or distribution board.

Are any protective devices tripping?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13

Re: LV Cables Fault Location

01/09/2012 8:42 AM

Here's really cheap....

Have you walked along the cable route yet.?

Look for disturbed soil or a conspicuously parked excavator......

Might be a backhoe fading problem.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#15

Re: LV Cables Fault Location

01/09/2012 10:55 AM

Several points are not clear:

1. What length of cable are we talking about? Since you say LV, which I assume means Low Voltage, it presumably is a couple hundred meters or less.

2. I do understand that English is not your native language... You say "layed on Ground one meter deep". To me, "Laid on ground" means "on the surface" of the ground. Yet "one meter deep" means it is buried in the ground.

3. As several other posters have indicated, we don't know whether the cable is in a conduit or directly buried.

Again as several other posters have indicated,the correct solution is probably not cheap. The correct solution is new cable in an appropriate conduit.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#16

Re: LV Cables Fault Location

01/09/2012 1:21 PM

What is this cable core earthing to? Is it wire armoured? Is it in a metal conduit? PVC insulated cable is not suitable for direct burying as someone has said.

You cannot get zero ohms through a cut in the PVC into damp soil. It will have a value. If it really is so low then something has hit it, look for new work, excavators, new posts in the ground.

"Phase to ground insulation is zero" has me confused, what is your ground? Is something tripping? If you can put a few hundred amps from a welder or a big truck battery across your fault you might hear a bang, or see some smoke coming up from the ground.

Register to Reply
3
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#17

Re: LV Cables Fault Location

01/09/2012 3:23 PM

Cheapest solution I have ever seen for finding the location of a fault was to hook up an electric fence unit ($100NZD:$75USD) to the damaged conductor and walk the line listening for the pulsating crack sound.

Plus you can use to breakfeed the sheep and cattle, or as kids we used to wire them to door handles.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#19
In reply to #17

Re: LV Cables Fault Location

01/09/2012 9:30 PM

That's pretty cool.

Do you reckon you could hear an arc cracking that's buried 1 metre below the surface? How deep were the damaged conductors buried when you witnessed this technique?

The cost estimate you quoted is for the cheaper portable units right?

There are high end market electric fence units that will display a DTF (distance to fault) value. Which is handy for larger permanent installation's performance monitoring and trouble shooting. With these you wouldn't have to hear the crack.

GA by the way. I'll remember that technique.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#18

Re: LV Cables Fault Location

01/09/2012 6:05 PM

Christle,I voted for you

Register to Reply
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#20

Re: LV Cables Fault Location

01/09/2012 10:49 PM

In NZ we bury LV to a nominal 600mm. So even buried at that the depth the sound was audible. Don't know about 1000mm given that sound will be about 2.8dB down.

Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 24
#21
In reply to #20

Re: LV Cables Fault Location

01/10/2012 9:21 AM

The fault locator must have a ground microphone like GM105 to hear the arcing.

JS

Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#22

Re: LV Cables Fault Location

01/10/2012 12:47 PM

I've just realised that if he has a dead short, zero ohms, then it won't crackle from the conductor to whatever earth this guy has. Blow it first with my welder/battery solution, that will create a gap which will spark & crackle later with a cattle fence supply.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#23

Re: LV Cables Fault Location

01/10/2012 5:47 PM

If the lines are buried you may as well replace all of them. What ever caused the one to fail (age of wire, manufacturing defect, moisture, rocks etc.) will most likely appear sooner or later in the other lines. We had a plant built in the 50's with lines in conduit and pull boxes. A main feed shorted out one cold wintery night. After working 4 days and nights moving snow and pulling wire we got it running again only to have another line fail about a month later

__________________
deanpavil
Register to Reply Score 1 for Good Answer
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cristle (2); deanpavil (1); dkwarner (1); dvmdsc (1); electricalexpert65 (1); engineertony (3); joseph sithole (2); KJK/USA (3); lyn (2); redfred (1); Rockyscience (1); SolarEagle (2); Wal (3)