Previous in Forum: Fuse for Neutral   Next in Forum: Electric Heaters
Contactor
01/17/2012 8:38 AM
iF I HAVE APPLICATIONS SUCH AS PLC, SAFETY CONTROLLER , RFID etc Can i use contactor/RELAY of utilization category DC-1?
Good Answers: 181
Re: Contactor
01/17/2012 9:28 AM
STOP SHOUTING FIRST!
India - Member - New Member
Good Answers: 164
Re: Contactor
01/17/2012 10:35 AM
What do you think the nature of your load is ? Resistive, inductive, capacitive....what?
You are not that new here ... you should know better than to use uppercase.
Good Answers: 170
Re: Contactor
01/17/2012 10:57 AM
KVS! I think PLC, etc. falls under Utilisation category DC-12 (Control of Solid State Loads with Isolation by Opto-couplers) vide Clause 4.4 (Table-1) of IEC 60947-Part 5 - Section 1.
Good Answers: 164
Re: Contactor
01/17/2012 12:09 PM
Thanks, but my intention was to make the OP do his own work. Even if one doesn't have a $1000 IEC standard with one, every contactor catalog gives the IEC Utilisation Category table. All one has to do is download and read.
Specific to your view, perhaps yes, DC12 may be the right one. i designed and tested everything in DC to DC13 anyway, why quibble ? Not much benefit in cost.