Previous in Forum: Teco Vfd   Next in Forum: Voltage Fluctuation Effects Star & Delta At First
9 comments
Distance Relay Facing Backward
03/12/2012 5:08 PM
Hello
My distance relay at a 132/33kV terminnal sub-station is tripping due to faults on 33KV feeders. My suspicion is that it is looking at the wrong side. How do I confirm and correct this please?
Re: Distance relay facing backward
03/12/2012 5:18 PM
Well you could check the wiring is correct, followed by the relay settings.
It is possible it is something as simple as incorrect wiring or settings.
03/12/2012 5:42 PM
What has changed since the commissioning records were taken, Boss?
Good moaning!
03/12/2012 5:49 PM
If your work force was so incompetent that they miswired a 33kV sub-station transformer by connecting 33kV to the 132V side then instead of stepping down the voltage to 132V you'd (briefly) step up the voltage to 8,250kV. No testing will be needed to detect this type of a fault, failure will be immediate and catastrophic.
So I don't think that this is what happened but it is the only scenario that comes to my mind that you are proposing. You see your subject in the second sentence is the undefined pronoun "it". This tells me that either you have given us a poor English translation of what you wanted to ask or that you know nothing about high voltage power distribution.
Only knowledgeable and authorized people should work on anything in a sub-station. Ask your on site engineer what to do. If their answer makes no sense to you, bring their answer to us and we will try to explain.
Good Answers: 131
03/12/2012 8:47 PM
Sorry, RedFred, but your reply is off-base here. A distance relay works by "looking" outward from a station along a transmission line, to see if there is a change in the impedance it measures (magnitudes and phase angles of the voltages & currents) caused by a fault. If the CTs or PTs are wired to the relay backwards, the relay will be "looking" into the station and seeing what's happening there, and could even look "through" a transformer to see what's happening on the secondary.
The OP needs to verify with the relay's instruction & operations manual that the CTs and PTs are connected in the proper polarity for the direction of fault detection. This should have been done at commissioning of the protective relay system.
03/12/2012 10:25 PM
That's fine with me. I misunderstood what the OP was talking about. I wouldn't say I was off-base.
I pointed out that the only thing I could grasp from the description was something that didn't make sense. That's hardly off-base to point out my own limitations. I next pointed to a nebulous pronoun use that lead me to think that this was about wiring a transformer. I then pointed out that only knowledgeable and authorized persons should work on a sub-station. I don't think that's off-base and I hope you feel that way, too.
Good Answers: 131
03/14/2012 7:23 AM
I'm sorry - I probably should have worded my reply differently. As you said, you misunderstood, and I should have put it that way. From what I have seen you have been one of the most knowledgeable contributors here on CR4. I only meant to say that you didn't understand what the OP was asking, and to someone who has worked with protective relaying more, his question did make sense (although some more detail would have been helpful). Keep posting! We need your expertise.
03/14/2012 10:36 AM
I thank you for the compliment and rest assured I will continue to post to CR4. That is as long as people tolerate my warped sense of humor.
03/17/2012 5:00 AM
What do you know mr Redfred. You make me sick with all your dumb comments. Did you ever think that maybe someone was observing and wanted to know the answer. It depends on which side the secondary point of the ct's are star pointed and then you have to tell the relay which side is star pointed. If you draw it out on paper it becomes clear. To prove the settings you have to do a dynamic test which involves adjusting the settings on load to make a healthy condition look bad and vice versa. Best regards
Good Answers: 22
Re: Distance Relay Facing Backward
03/14/2012 3:13 PM
isatanimu,
The distance relay will have a few protection elements looking in the forward direction (towards the OHL) and one element looking in the reverse direction (towards station busbars / transformer). The reverse looking element is set with low impedance value so that it cannot see faults in the 33kV side of the transformer and limit its operating zone for faults in 132kV busbars / 132kV windings of the transformer. The element also is time delayed.
In your case, it is possible that the reverse looking element is set to see in to the 33kV system but the time delay is not coordinated with the Transformer O/C protection operation.
If you could review the impedance setting calculation and the basis for time delay settings, the issue should become clear.
Trust the above is helpful.
Raghunath
Register to Reply 9 comments