G.I Earthing Strip Coating

03/13/2012 12:45 AM

what micron Galvanium coating is done on strip as per the standard? we have a bit corrosive chemical plant where we faces problem of rusting in G.I Earth Strip. can bitumin layer be applied on it for some rusting protection? if yes are this covered in standard practice?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: G.I Earthing Strip coating

03/13/2012 1:14 AM

What standard?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: G.I Earthing Strip coating

03/13/2012 7:11 AM

Is bitumen a good conductor?. It should not act as a barrier between the metal earthstrip and the ground.

__________________
pnaban
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#3

Re: G.I Earthing Strip Coating

03/13/2012 11:01 PM

I presume that by "Galvanium", you mean zinc. Galvanized Iron is iron coated with zinc. When you say "G.I. Earth Strip", is this strip inside a machine or junction box, or is it in contact with the earth (ground, soil)? If it is in contact with the soil, it should be heavily copper coated, not zinc coated. Definitely NO on the bitumen! Tar (bitumen) is an insulator, and would defeat the purpose of the earth/ground connection.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#4

Re: G.I Earthing Strip Coating

03/14/2012 12:02 AM

I hope these links will help satisfy your curiosity.

Grounding Electrodes-http://www.nachi.org/grounding-electrodes.htm

Commercial Grounding Installations-http://www.sankosha-usa.com/pdf/san-earth-tech.pdf

Since you don't know very much about electricity, you should put this project into the hands of a qualified electrician. Improper grounding can result in extensive property damage and loss of life.

Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#5

Re: G.I Earthing Strip Coating

03/14/2012 1:25 AM

if the GI earth strip is connected to the actual earthing bar than it is ok to insulate with what ever means .In some places GI coated steel cables are used instead of insulated cables due to cost or deter thefts. what ever done the end result is you must get the required min earth resistance to meet your installations requirement.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: G.I Earthing Strip Coating

03/14/2012 11:11 PM

If strip is not insulated the area in contact with earth increases and measured resistance will be less.

__________________
pnaban
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#7
In reply to #6

Re: G.I Earthing Strip Coating

03/15/2012 12:12 PM

I belief the galvanised strip is just acting as a conductor from the frame to the actual earth rod/earth bar at the earth pit.Even if bare copper conductor were to be used than in no time that too would become ineffective due to oxidation .

Register to Reply
Register to Reply 7 comments