Motorized Valve Selection in AHU

03/18/2012 6:17 AM

I want to know how we can get the cooling coil pressure drop in a chilled water line.

Incoming pressure is 10bar

Water side pressure drop of AHU is 12.93 kpa.

Motorised valve is 2 way control valve with a bye pass line with gatevalve .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Motorised valve selection in AHU

03/18/2012 9:18 AM

Measure pressure of cooling water at the inlet and at the outlet and subtract. That will give you the pressure drop across the cooling coil.

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#2

Re: Motorized Valve Selection in AHU

03/19/2012 1:48 AM

Thanks Lyn.

Yes , I got the pressure drop - the AHU supplier has provided me the designed value. It is 12.93kpa. Then I used this value to find out the total pressure drop in the line. Adding the drops at 'Tee','Gate Valve', 'Y- strainer', 'reducer', etc in the line by taking into account the equivalent pipe length as per the "carrier table 10 & 11". This calculation is given to the supplier of 2way motorised valve, which controls the chilled water flow to the coil inside the AHU. But when this valve supplier tried to put the value in the valve selection software , it shows error. The software is not able to select a valve size for the calculated value of pressure drop.

There is a chance that the method of calculation of pressure drop can be wrong.

Can anybody help me to correct the error.

Thanks in advance.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Motorized Valve Selection in AHU

03/19/2012 4:33 AM

Discuss it with the supplier, then. You do have a telephone, don't you?

__________________
Good moaning!
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Oct 2011
Posts: 95
#4

Re: Motorized Valve Selection in AHU

03/20/2012 7:34 AM

Yes , I tried with supplier , AHU supplier has given the pressure drop in coil . Then I calculated the total with equivalent length (m) for all "tee", valve ,etc . Then I put all values in "Pressure Drop Online-Calculator" of www.pressure-drop.com . Then I got the result .

Thanks

Register to Reply