Upstream Breaker/Fuse for Surge Arrester

03/29/2012 9:40 AM

Dear All,

I have selected a Surge arrester for a MCC (FLT-CP-3S-350, Phoenix contact) but I am confused about two things.

- Max. continuous operating voltage is 350VAC, this means that if the line voltage is above 350V will it drain to earth? Our supply voltage is 400VAC.

- Max. back up fuse according to the catalogue is 315A(gL/gG). Do I really need that size fuse? Max. cable size I can connect to arrester is only 25mm².

Please advice.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Upstream Breaker/Fuse for Surge Arrester

03/29/2012 10:42 AM

1) Maybe, after a while. What happens if you use it continuously at greater than 350Vac is unspecified. Select another surge arrestor.

2) You can use any fuse you like with this arrestor, as long as it is less than or equal to 315A. That's why it says "Max.".

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Upstream Breaker/Fuse for Surge Arrester

03/29/2012 1:41 PM

You have selected a 350VAC arrester for a 400VAC supply ??

You are not qualified to select anything here. Hire someone to help you before you injure (or worse) yourself or others.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Upstream Breaker/Fuse for Surge Arrester

03/30/2012 12:52 AM

If my guess is correct, the surge arrester would have been connected between phase and earth and not between phases. If true, the phase-to-earth voltage in a 400V system is 230V and thus there may not be any problem with 350V arrester.

The fuse is selected to protect the cable in case of feeders and to protect the arrester in case of surge arrester. Thus the fuse rating doesn't depend on the cable short time withstand and instead on the discharge rating of the arrester.

Hope the above is helpful.

__________________
Raghunath
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: Upstream Breaker/Fuse for Surge Arrester

03/30/2012 7:38 AM

Phase to ground is ok with selected device.

Phase -to- phase will of course, require an appropriate higher rating. However, most systems use 3 Mode protection,which includes phase to phase protection as well as phase to ground, and ground to neutral.The fuse is used to prevent catastrophic failure of the surge suppressor. They are designed to absorb a very brief surge, but sometimes they will weld in the shorted condition and if not fused, they will explode and cause further damage.

The status of a surge suppressor can not be determined by looking at it.

Size your fuse to protect the wire feeding the surge suppressor.A quick acting non time delay fuse is recommended.An excluder type fuse holder is recommended to prevent replacement with a standard fuse.

I recommend a neon indicator(with proper resistors in series) across each suppressor.When light is on, suppressor is ok.

These indicators should be panel mounted so as to be readily visible externally.

If light is off,a failure has occurred and the suppressor must be replaced.These devices are good for one-time only, and are not reliable after absorbing a surge.

Hope this helps.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 12
#5

Re: Upstream Breaker/Fuse for Surge Arrester

04/02/2012 12:59 AM

Dear All,

Thank you very much for your comments.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); JohnDG (1); kra101 (1); raghun (1); WJMFIRE (1)

Previous in Forum: Landscape Lighting Selection   Next in Forum: Cooling Fan Earth Connection

Advertisement