Panel Design

03/31/2012 1:42 AM

if i will use MCB(with conactor) in place of MPCB....what will happen?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: panel design

03/31/2012 7:27 AM

Then you cannot achieve Type-2 Co-ordination for the motor feeder. With MCB it can only be a Type-1 Co-ordination. During a short circuit, may be the contactor and other components of the motor feeder will damage. Also, the bimetallic element in an MCB is not designed for motor protection. It is designed for feeder protection of cables. Hence, an MCB in place of an MPCB is NOT ADVISABLE.

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: panel design

03/31/2012 7:54 AM

So what is adviceable, should i throw my MCB?

I think MPCB are fuseless replacement of MCB & Relay..!

Register to Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: panel design

03/31/2012 9:49 AM

Throwing your MCB or keepint it in a museum is your worry! I can only give technical advice here. MPCB is NOT a replacement for MCB and Relay. It is a replacement for Switch-Disconnector-Fuse-Unit and Thermal Overload Relay. During a severe short circuit, a fuse would operate in under 5 milliseconds, but an MCB may take about 10 to 20 milliseconds. Moreover, an MPCB's Overload I-t Curve is exactly matching that of the thermal overload relay, whereas an MCB's overload curve would not match that of the thermal overload relay. Now, the choice is yours.

Register to Reply Good Answer (Score 2)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Panel Design

03/31/2012 1:37 PM

If you didn't get it from what ElecExpert said, you don't have to throw out the MCB but you cannot use it with just a contactor, you will need to use a contactor AND a thermal over load relay.

Another issue however is fault capacity. In an MPCB, the ability to safely interrupt a fault is usually very high, often around 65kA, whereas in an MCB it is usually very low, often around 10kA. That is a significant factor in industrial controls. MCBs are Cheaper because they are residential devices that can SOMETIMES be used in light industrial applications, but that was not their designed intent.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Member

Join Date: Mar 2012
Posts: 8
#5

Re: Panel Design

04/02/2012 1:48 AM

thanks friends....very useful information for me

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ashishraj1433 (1); electricalexpert65 (2); JRaef (1)

Previous in Forum: I Want To Learn About Lamps Fluorescent, CFL And HOX....   Next in Forum: What Does FAR Stand For?

Advertisement