Hi Guys
I have two transformers 22KV/400V star connected on the secondary side supplying Substation A. In Substation A we have two main circuit breaker supplied by the two transformers with a bus-coupler in-between(meaning three, 3ph Master pack circuit-breaker) for incase we have problem on one incomer we can use the bus-coupler to supply other side. From subsation A I have two feeders/supplies which supplies Substation B, and substation B has the same set up like substation A (meaning Substation B have two incomers from Substation A. three, 3ph master pack circuit breaker which one is a bus-coupler).
The neutral bars of both transformers are linked/connected together at Substation A and Substation B MCC.
The two Circuit breaker that supplies sustation B at sustation A are eguipt with earth leakage relay (1000mA New Elec).
THE LOADS THAT ARE SUPPLIED BY BOTH SUBSTATIONS MCC'S ARE 400 V AND 230 V
PROBLEM: The two Circuit breaker that supplies Substation B keeps on tripping on earth fault due to the coupled neutral bar.
Solution: We decided to un-couple/remove the link that link the two neutral bar at Substation A to solve the tripping problem. And if we have a problem with one Transfomer or Incommer one must first couple/connect the two neutral and close the bus coupler.
Question: If one transfomer/Incommer has a problem, What will happed if the bus-coupler is closed to suppler other side without connecting/coupling the neutral bus-bar.
REMEMBER I HAVE 230 VOLTS LOADS ON MY CIRCUITS.
Please Help.