Anonymous Poster

Electrical Engineer

05/09/2007 4:16 AM

What is the maximum allowable resistance for grounding system of electrical equipment protection against shortcircuit and overload?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member

Join Date: Feb 2006
Posts: 962
#1

Re: Electrical Engineer

05/09/2007 7:20 AM

IEE 16th edition requires that the minimum conductor size be half the size of the main earthing conductor, for 100A installations a main earthing coductor of 16 mm2 and a bonding conductor of 10 mm2 will meet requirements where the supply neutral conductor is not more than 35 mm2 It is recommended that the earth fault loop impedance does not exeed 220 Ohms. Taken from IEE on-site guide.

__________________
There's them that knows and them that just thinks they know, whitch are you? Stir the pot and see what rises up. I have catalytic properties I get a reaction going.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Electrical Engineer

05/09/2007 3:41 PM

It depends on the countries local standards & regulations and the specific application (intrinsic safety earths for a hazardous area installation have a lower limit than say a houshold earth system).

More information is necessary.

__________________
jack of all trades
Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#3

Re: Electrical Engineer

05/10/2007 1:59 AM

It depends on the location and Country govt rules. For example (Industiral) in dry areas in India should be less than 2 ohms and near sea shore 0.5 ohms max.

__________________
Subramanyam
Reply
Anonymous Poster
#4

Re: Electrical Engineer

05/10/2007 7:57 AM

3 ohms

Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#5

Re: Electrical Engineer

05/10/2007 8:18 AM

Check German VDE they have very specific requirements for many of grounding systems.

Reply
Member

Join Date: May 2007
Posts: 6
#6

Re: Electrical Engineer

05/10/2007 10:03 AM

It actually depends on type of grounding needed. Most installations, and codes, lean toward low resistance grounding to facilitate braker triping in the case of a phase to phase or phase to ground fault. But there are installations that require high impedance grounding. This impedes breaker trips in the event of a fault for situations where shutting down a process is more detrimental then shortening equipment life. Check out www.i-gard.com for resources on this topic.

Reply
Anonymous Poster
#7

Re: Electrical Engineer

05/10/2007 11:57 AM

This is dependent upon the country and municipal regulations. In the US, it is 25 ohms between the ground and the electrode.

Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#8

Re: Electrical Engineer

05/10/2007 10:24 PM

What about The Computer? One Ohm?

What about common with lighting protection?

What about section of the grounding grid / web?

Reply