Hi

I have an off grid inverter 12V/220V/600W (modified sine wave type), battery bank of 100Ah/12v/c20 wet solar battery and PV solar panels of 150W. From inverter's user manual, instructs to ground an inverter for the earth terminal shown, I have done so, when you use an AC electric tester (the simple tester used to know if part of installation (domestic) is live), at the 220VAC side of it, at the neutral terminal, the tester lights up, as it do for live terminal. What might be the problem? And if so how to rectify it?

Register to Reply
Pathfinder Tags: off grid POWER INVERTER
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: OFF GRID 12VDC/220VAC INVERTER

04/19/2012 4:47 AM

Modified sine wave is a harmonic mess with high (detectable) spikes, plus the terminal you are grounding is possibly the battery (-), and nothing to do with ANY grounding on output. That, is supposed to be floating, so no problem if you grounded one of the output rails, and see it not triggering testers. But I'd check for leak currents before even trying, and would only try it, If I had a reason (like powering a suffering from interferences or already ground-leaking appliance). S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#2

Re: Off Grid 12VDC/220VAC Inverter

04/22/2012 11:09 AM

You say "the simple tester used to know if part of installation (domestic) is live)"

What sort of tester are you referring to ? do you mean a non contact voltage tester like a volt stick ?

If so most of the non contact voltage testers I have used will indicate AC voltage on neutral wires

Try using a multimeter you will get a more accurate reading

Register to Reply
Associate

Join Date: Sep 2010
Posts: 45
#3
In reply to #2

Re: Off Grid 12VDC/220VAC Inverter

04/23/2012 4:23 AM

Yes,I mean this tester.But also I have used a multimeter,L to G it reads 143VAC and N to G it reads 143VAC,L to N reads 230VAC.The -VE terminal of a battery is Grounded.