Local Breaker for Large Transformer (20MVA)

05/09/2007 8:39 AM

What is the maximum length of 33kV cable that can be used for connecting 20 MVA transformer without having a local isolation breaker??

Thanks

SC RAICH

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member

Join Date: Feb 2006
Posts: 962
#1

Re: local breaker for large transformer (20MVA)

05/09/2007 9:41 AM

Virtually none. The idea is to both protect the cable, and the transformer against a fault condition. Big transformers cost a lot and most faults occur on the cable side of things.

__________________
There's them that knows and them that just thinks they know, whitch are you? Stir the pot and see what rises up. I have catalytic properties I get a reaction going.
Reply
Member

Join Date: Dec 2006
Posts: 8
#2
In reply to #1

Re: local breaker for large transformer (20MVA)

05/09/2007 11:56 PM

ARe we talking about the cable on the primary or the secondary side? The cable on the secondary side could be as long as you wish provided the primary protection and isolator operated for faults in the transformer or in the LV cable and the downstream LV distribution upstream of the next isolator.

Similarly, the cable on the primary could also be as long as you wish provided it is covered by a protectiv zone.

Now, 'voltage drop' in this long cable is another cat altogether.

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: Local Breaker for Large Transformer (20MVA)

05/16/2007 12:22 AM

I expect that the transformer is 33/ 0.44 KV step down one.

The basic requirement of Circuit Breakers in Electrical Distribution system is to cut off power supply before effecting any type of damage to the costly equipment and prevent fire and accidents .

The normal fault on cable is earth fault short circuit and the fault level depend on the current and voltage rating and length of the cable . The 20 MVA transformer have to be protected for over current earth fault and over temperature ,for this control cable have to be laid to the breaker from transformer.

Hence the maximum distance will depend on all these factors.

Reply