Anonymous Poster #1

Surge Protector Selection

04/23/2012 12:17 AM

MOV surge protectors in its specification says its Up (Threshould voltage ) as

ex- at 1kA-1.2kV

at 5kA-1.4 kV

at In- 1.8kV so on.

can anybody elaborate this. ??

How do we select the Up according to the level of DB. (i.e- Main panel , Distribution boards and sub DB levels)???

Thank You.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Surge protector selection

04/23/2012 8:17 AM

If you will investigate a bit, I think you will be able to answer your own questions. I like to shop here for components but you may have some other distributor closer to you.

These devices protect by providing a short circuit path for excessively high voltages up to their current rating but only for a very short time. Fortunately, most surges are in fact, very short. But, if they persist, the MOV will burn out (we like to call that "letting its smoke out"). Unfortunately, you will only know this has happened if you check.

Some manufacturers have a detection circuit to determine the status of the MOV. I would expect it to be some form of pulse injection but I don't have any real design information.

I can tell you that the most common mistake made with surge protection is placing it too far away from the source or the actual load you intend to protect. You want the MOV to be installed one of the shortest paths between power conductors. On a Main Panel, this would be right where the power cables are attached. On a distribution board, this woulld be right where the power comes in.

By the way, because these are so inexpensive, it is better to have a few extra in parallel. That will assure a longer service life.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Surge Protector Selection

04/24/2012 10:58 AM

Please refer to IEC 60364-4-443