Temperature Sensors In Parallel Connection

05/08/2012 9:28 AM

Dear Forum members, I have 2 nos. parallel connected battery banks with a NTC (negative temperature coefficient) thermistor sensor attached to each battery bank. I need your expert advice if I can connect both these thermistors in parallel and take 1 input to the temperature compensated regulator ( charge controller). Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Temperature Sensors in parallel connection

05/08/2012 9:56 AM

No!

Well actually you can do this. Nothing will explode, or be damaged in any fashion by connecting these two sensors together in parallel. You just won't have any useful information from doing this. A NTC thermistor means that the resistance will decrease as the temperature increases. By connecting the two thermistors in parallel you will immediately make the electronics record an extremely hot temperature condition. If this thermistor is part of a feedback system then you may damage something though.

Now if (and a very big if) the electronics recording range, the nominal expected temperature and the nominal resistance of each thermistor happens to put everything in the correct range with the two thermistors wired in parallel then this is possible. However, to do this properly you'd need to have a good understanding of circuit theory, particularly Kirchoff's laws and Norton's mesh analysis to assure a working system. If you already understood this, then you wouldn't be asking this question.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Temperature Sensors In Parallel Connection

05/08/2012 10:29 AM

If the thermistors are of the same type, you may get away with it by getting two more, and putting them in series with the existing ones, then connecting the two pairs in parallel (giving the same overall resistance as one thermistor when all at the same temperature.

But it's a very big "may"; there's no saying how well the charging process would be controlled without a detailed analysis of the charging circuit, batteries etc.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: Temperature Sensors In Parallel Connection

05/08/2012 5:50 PM

Don't do it!!!

For all the reasons already explained, plus since they are in parallel and the resistance will be split, the apparent temperature would be some sort of "average" of the two.

You could have one hot spot (boiling) and one ordinary and the output would indicate an apparently safe temperature.

Just do a Boolean table of some possible temperature states for the sytyem and you will see that the results will be meaningless. (That is multiple input conditions will give the same output signal.)

If you have only one reader, then multiplex the thermisters and read tehm independantly.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: Temperature Sensors In Parallel Connection

05/08/2012 7:07 PM

"You could have one hot spot (boiling) and one ordinary and the output would indicate an apparently safe temperature.".

I thought this one through, but as their resistance decreases with increasing temperature, the parallel combination resistance will be dominated by the lower resistance at the hot-spot[1], so it would control to safety. It wouldn't, however, necessarily do much good charging the two banks optimally.

Also, monitoring the voltage of and current into each bank would be some kind of horrible average or somesuch.

Good thought about multiplexing, but it would need a pretty special controller - probably cheaper (and safer) to just get two controllers.

</ramble>

[1] my "series-parallel combination" assumes that the two thermistors in each leg (i.e. in each bank) are both heated by the batteries.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Temperature Sensors In Parallel Connection

05/08/2012 9:47 PM

For any battery bank a single thermistor is useless (going from your previous posts these are large scale units).

If you're going to be doing this seriously each cell needs to be monitored. While the ambient temperature of a bank seems OK, one cell could be boiling away unnoticed.

To my mind you need to rethink the whole scenario.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Temperature Sensors In Parallel Connection

05/08/2012 11:53 PM

In modern times you let an inexpensive microprocessor collect and collate many measurements for you. If all are ok, fine. If not dig down. The data is there.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 21
#7

Re: Temperature Sensors In Parallel Connection

05/09/2012 12:16 AM

Thanks friends for the information, I think the best is to have 2 controllers, 1 for each battery bank and then connecting to the load bus in parallel.

Register to Reply