Problem With Periodic Overvoltage Surges

05/08/2012 1:01 PM

Hello everyone

warm regards for the day

I am an electrical engineer working in a thermal power plant, wherein as a part of our distribution system we have an ACDB (AC Distribution Board ). Itis powered up by two incomers coupled through a bus coupler (each with a capacity of 800 A). Right now both the incomers are in charged condition through which the bus is charged. Each Incomer drives its corresponding loads which include three variable frequency drives each. Off late, the VFD's driven by the first incomer are getting tripped and the VFD error which is displayed on its screen symbolizes tripping due to Overvoltage. This has been happening for few days and the drive gets tripped atleast 2-3 times a day. The incomers are inturn powered up using two dry type transformers (2MVA) which have a solidly grounded neutral.We have checked the neutral if its floating but found out that its solid grounding is proper. What might be the other reasons for these overvoltage surges?

Thanks and Warm regards

__________________
mscs
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Problem with periodic overvoltage surges

05/08/2012 1:08 PM

If you have, "two incomers coupled through a bus coupler", how can they operate independently?

Since you are an electrical engineer, do you have any thoughts on the subject?

Register to Reply
Associate

Join Date: Feb 2011
Location: Angul, orissa
Posts: 25
Good Answers: 1
#2
In reply to #1

Re: Problem with periodic overvoltage surges

05/08/2012 1:15 PM

The bus coupler would be in OFF condition under normal conditions. In case I want to do some maintenance work on one of the two transformers, I can switch off the incomer which is being powered by that transformer and charge the bus through the other incomer and the bus coupler.

__________________
mscs
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Problem With Periodic Overvoltage Surges

05/08/2012 2:20 PM

OK, let's go another route.

Have you done anything to try to solve the problem, other than come here and ask for help?

If you have done anything to try to solve the problem, other than come here and ask for help, what was it?

Can you add any more information the meager trickling offered so far?

Register to Reply
Associate

Join Date: Feb 2011
Location: Angul, orissa
Posts: 25
Good Answers: 1
#4
In reply to #3

Re: Problem With Periodic Overvoltage Surges

05/08/2012 2:38 PM

1) We have checked the transformer neutral (to find out if its floating or if its effectively earthed)

2) We have cleaned all possible insulating supports (in case theres some tracking because of dust and in case if the neutrals floating then there is a chance of overvoltahe in the system)

3) We have tightened all the nutbolts of the power cables (to avoid sparking)

4) We have meggered the cable which connects the incomer and transformer. (again faulty cable and a floating neutral may lead to an overvoltage)

__________________
mscs
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12
In reply to #4

Re: Problem With Periodic Overvoltage Surges

05/11/2012 9:40 AM

Dear MSCS,

You have mentioned that normally bus-coupler is kept in OFF condition i.e.,one 2Mva trasformer catering the particular drive loads thro' one incomer. Please mention the distance of MCC panel to motor i.e., the length of the cable connected betn.MCC panel to motor .For higher length of cables, inductors are used to mitigate generation of higher voltage due to Ring effect(for PWM Drives). Please take care of the above and hope ,your problem may be solved.

Thanks,

Manindra

__________________
Manindra
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Problem With Periodic Overvoltage Surges

05/08/2012 3:10 PM

Have you checked what is the actual voltage at the two transformers that feed the two ends of your distribution panel? Maybe the source for one of them actually has an overvoltage. Until you rule that out, there may be a good reason your VFDs are tripping.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#6

Re: Problem With Periodic Overvoltage Surges

05/08/2012 4:23 PM

Hate to spoil the surprise but VFDs don't overvoltage trip from power side only, sometimes OV comes from load side (what they see as load anyway). First make sure on what is the OV source. And are any PFC caps on line at switching time? S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#7

Re: Problem With Periodic Overvoltage Surges

05/08/2012 5:45 PM

Your stated observation that all three VSDs trip (and I assume they are tripping at the same time) suggests to me that the problem is "real" and is from the supply side. If it was a load problem, then you would expect only one to trip.

I would expect that the operational power station would have appropriate monitoring devices that could be connected to monitor the infeed and confirm the waveform/voltage/phase match for the suspect feeder.

Is there a tap changing transformer in the feeder? Maybe the transients are causing the trip.

Is there one large load that "dumps" and the transformer reaction spikes the other VSDs?

What else is on that "network" that could cause transients?

Have you run the system for prolonged time of the single "good" feed?

Are the trips happening at shift changeover or some other significant time in the operation of the facility?

do the VSDs have proper protection to stop them affecting the incoming supply waveform (and thus tripping the others)?

There are many investigiations that you still need to do and please be assured you will find the answer by following good Engineering practice.

Define the problem (in time and space. What, When, Where, How often, etc)

Look at what has changed, or whether the problem existed since the plant was commissioned. (like service of the transformer or exchanged for maintenance.)

Determine hypothesis for possible failure modes.

Test (desktop review) whether those failure modes match the What, when where etc conditions.

Verify this by removing that stimulus or altering it in a controlled manner.

CHECK the results again and test any other viable causes. (Rarely there are two together.)

Verify again.

Take steps to correct the identified disturbance.

Take steps to make sure that the same thing doesn't happen in other processes (Like your other transformer feed.)

Good luck. Enjoy the journey.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#8

Re: Problem With Periodic Overvoltage Surges

05/08/2012 8:44 PM

:)

need your more information :

1. are these 2 transformer get from one source ?, if not you must check carefully on both voltage and frequency

2. If these come from one source, are these transformer has the same spec ie. brand, vector group, step voltage ?, must have same output.

3. Please check with coupler open with no load, both output voltage-Must has the same output of voltage. And try to load on each transformer with isolated from other of course and compare with load on the other, their must have the same point of value, if not - could be one of this transformer drive the fault.

__________________
One system
Register to Reply
Member

Join Date: Jan 2012
Posts: 9
#9
In reply to #8

Re: Problem With Periodic Overvoltage Surges

05/08/2012 11:48 PM

May be tripped VFD in load side . you cheak load side and breaking resister.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Problem With Periodic Overvoltage Surges

05/09/2012 5:20 AM

If you monitor every vital component in the system bu trips/alarms you can avoid disasters like fire/explosion. It is advisable to include duplicate components to avoid power failure.

__________________
pnaban
Register to Reply
Associate

Join Date: Oct 2011
Posts: 29
Good Answers: 2
#11

Re: Problem With Periodic Overvoltage Surges

05/10/2012 10:45 PM

Do you have a surge protection device installed ? Several clients have reported solving the tripping problem after having installed a set of SPD's. Their VF Drives have been often tripping for inexplicable reasons. If interested, can send you a paper on SPD usage with VFD's from Phoenix Contact.

MADHAV

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Just an Engineer (1); kandasamy1979 (1); loadshare (1); lyn (2); madhavdivya (1); manindra (1); MSCS (2); PeterT (1); pnaban (1); SimpleMind (1)