Heat Detector

05/19/2012 10:37 AM

Dear Experts,

We are facing a problem please help me.One heat detector is installed in the plant inside the Exaust compartment of a turbine and commissioned also.Now operators are complaining that because of the end of line resistor(EOL),error is comming.we fixed the EOL as per the vendor recommendation...how could EOL give error...and if so what will be the solution.I will appreciate if anybody gives helpful reply

Thanks

Rajiv

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Heat detector

05/19/2012 11:19 AM

It would definitely be easier for us to accurately answer your question if we knew several additional things here.

  • What did your vendor say to do?
  • Did this repair work?
  • What type of thermal sensor are you using?
  • What electronics package is reading this sensor?
  • How far away is sensor and electronics?
  • Is the sensor in the exhaust stream itself or attached to the exhaust manifold?
  • What is a nominal probe temperature?
  • Does this EOL error signify a signal loss, out of range reading or just a precision error?

Without knowing these answers one can only guess what is going on. I suspect that your EOL error is just telling you that your thermal sensor is disconnected from your electronics.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Heat detector

05/19/2012 12:32 PM

The EOL resistor cannot be mounted in the exhaust tunnel; it will not be rated for this environment.

Solution:

1. Mount a junction box outside of the turbine enclosure with a 4 double row terminal barrier strip inside.

2. Run a pair of wires from the detection circuit in the control panel to this box; terminate on terminals 1 and 2.

3. Run a pair of armored, braided temperature rated conductors (exhaust tunnel will be 450-550 F during operation) from terminals 1 and 2 "out" to the detector (must be a 4 wire device, explosion proof, rated 600 degree F).

4. Run another pair of high temperature conductors from detector (other two wires on detector) back to junction box and terminate on terminals 3 and 4.

5. Mount EOL resistor on opposing terminals 3 and 4.

If this is not what the vendor recommended, get another vendor.

Also, if this detector is tripping a suppression system (exhaust tunnels have bearing oil which can create a very intense fire) use two detectors and wire with logic such that both must be in alarm at the same time to discharge suppression agent (make terminal strip in box above 8 terminal and repeat sequence).

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Register to Reply 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: About Silver and Copper Corrosion Monitoring   Next in Forum: What is the Purpose of a Diode and Resistor in a Manual Call Point?

Advertisement