20P5 Testing for CT

05/24/2012 12:29 PM

Dear All,

I need to do CT burden test to check whether it is according to 20P5 rating. That is I have to apply 20 times rated primary current and have to check whether the output error is below 5%.

The rating of the CT is 125/5A. I am afraid to apply 20 X 125A by thinking it can cause a damage to CT. If it is OK, how much time I can apply 2500A. Will it be safe if I am applying that much current for 1 minutes.

__________________
If you can't find a way, make one........
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 20P5 testing for CT

05/24/2012 12:43 PM

If the test procedure isn't documented, it is of no use at all.

Follow the applicable test procedure and you will be fine.

If you don't have the applicable test procedure, get it.

Register to Reply Score 1 for Good Answer
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#12
In reply to #1

Re: 20P5 testing for CT

06/18/2012 12:15 AM

My dear, are you aware about you say ?

My question is how to check and confirm one CT's class.

IEC standard for CT testing is 60041. Even in the standrad it is only mentioned that accuracy limiting current should be found at rated frequency and rated burden of the CT. There is no description about, how to check or confirm the accuracy limiting current.

That is why asked how can I confirm the class of the CT.

Is it clear for you ?

__________________
If you can't find a way, make one........
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: 20P5 Testing for CT

05/24/2012 3:35 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#3

Re: 20P5 Testing for CT

05/25/2012 10:01 AM

It is obvious that you do not know what you are doing or saying . . . so do not do it - as you may hurt yourself. I trust you are someone who has filed his EE exams and not working int he industry.

An IEC expression "20P5" does not exist. If it did exist - it would mean 20% error @ 5 times overload, . . . and not what you are saying.

What you are doing is most likely a home-work assignment. So - do your home-work first, . . . and decide if you want to do the actual test later.

Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#4
In reply to #3

Re: 20P5 Testing for CT

05/25/2012 11:04 AM

I agree with you. I made a mistake. It should be "5P20" class. So how much time I can safely apply 20 times rated current ? Because I don't need to damage a good CT.

As you told, I don't know about it.. That is why I am asking. Otherwise my question will not be here.

I am working in the field of calibration more than 2 years. But I never done the test for CT.

__________________
If you can't find a way, make one........
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#5
In reply to #4

Re: 20P5 Testing for CT

05/25/2012 11:28 AM

No one in their right mind would apply 20 x rated current to any electrical equipment for 1 minute - as you suggest. Such a test will not only damage the equipment (CT) - but it will blow up in your face . . . Such overload test are typically done for 5-6 cycles (0.1 second) at the most, . . not seconds . . never minutes . . .

Also, no one would do such an overload test without first calculating the approximate performance of the equipment.

So, first measure the excitation characteristics and the winding resistance of the CT, . . . then calculate it s performance, . . . then decide if your really want to do the test. You will need some fine test equipment in order to the test and get the test data.

I suspect that you do not even know how to calculate the CT performance . . . . therefor you might want to buy, borrow or steal a "CTERP" from ELTEL Instruments (Bangalore) and have the "CTERP" provide the information for you.

Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#7
In reply to #5

Re: 20P5 Testing for CT

05/26/2012 9:00 AM

thanks for your valuable advise. BUT WE DON'T NEED TO STEAL SOMETHING WHICH WE DON'T HAVE. MAY IT IS THE CULTURAL DIFFERENCE OF BOTH PLACE. Anyway I have Omicron VE000656 and Soken micro ohm meter. I have CT secondary winding resistance value, excitation curve, knee point voltage and maximum applicable voltage for excitation test. From these data how can I find whether it is according to 5P20 class ?

__________________
If you can't find a way, make one........
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#8
In reply to #7

Re: 20P5 Testing for CT

05/26/2012 10:08 AM

Cr4 Admin: comment removed as it was an attack on a user. Please see cr4 rules of conduct http://cr4.globalspec.com/faq/cr4rules

Register to Reply Off Topic (Score 5)
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#9
In reply to #8

Re: 20P5 Testing for CT

05/29/2012 8:36 AM

See even your post is removed by the administrator because of your misbehaviour.

Even if you have good knowledge, you can't aquire respect if you don't know how to behave.

Anyway try to get some training to improve the behaviour.

Good Luck.

__________________
If you can't find a way, make one........
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: 20P5 Testing for CT

05/26/2012 12:37 AM

The guy must have a death wish.

Having seen a CT (100/5) explode under 10X load for 1 minute, I don't want to see it again. It was a test, but we weren't testing the CT, it failed before what we were expecting to fail.

It was in a safe zone, so no access.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - Justin Anto Engineering Fields - Electrical Engineering - Marks never made me laugh, but good memories did

Join Date: Sep 2010
Location: Thrissur, Kerala, India
Posts: 177
Good Answers: 3
#11
In reply to #6

Re: 20P5 Testing for CT

06/18/2012 12:06 AM

"The guy must have a death wish"

I think you are out of common sense. Because in my question itself I mentioned that "it may be dangerous". That is why I asked. The intention of the question is to get a method to check 5P20 class and not to execute the wish.

__________________
If you can't find a way, make one........
Register to Reply
Active Contributor

Join Date: Jun 2012
Posts: 22
#10

Re: 20P5 Testing for CT

06/07/2012 1:53 PM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Associate

Join Date: Feb 2009
Posts: 35
#13

Re: 20P5 Testing for CT

06/18/2012 1:38 AM

As I understand your requirements, you are check testing an already manufactured protective CT to ensure that its errors comply with the nameplate rating for commissioning / application purposes.

You are not designing/manufacturing a "new CT" & you are not trying to determine the CT's short circuit withstand dynamic capability.

There are two types of composite error tests according to IEC60044-1, type test for "new CT" design & routine tests for an already type tested CT.

The indirect routine composit error test is detailed in clause 12.6 & by simply energising the secondary winding you can ascertain whether the composite error is within class 20P5.

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amnakhan1245 (1); Instruform (1); justinanto1987 (5); lyn (1); olehwi (3); SolarEagle (1); TonyS (1)

Previous in Forum: Voltage Level   Next in Forum: Wind Turbine Generator

Advertisement