Previous in Forum: Constant Percentage Impedence of Auto Transformer   Next in Forum: Why Motor Start Current (DOL start) is 4-7 Times of Its Rated Current?
Close
Close
Close
11 comments
Rate Comments: Nested
Active Contributor

Join Date: Jun 2012
Location: Guwahati,India
Posts: 19

HT Motors

06/08/2012 1:30 AM

HT motors are not allowed large starting currents and their starting time is also large.

i want to know that which is the cause and which is effect i.e due to limiting starting current statring time is delayed or is it that due to delayed starting starting current is controlled to prevent windings from burning.

please help....

__________________
In search of the truth
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: HT motors

06/08/2012 1:37 AM
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: HT motors

06/08/2012 3:00 AM

"HT motors operate on high voltage ( 6.6 or 11KV). IF we make delta connections than voltage experienced by windings will be line voltage, which will require more insulation of winding. In star connection voltage experienced by each winding is phase voltage hence less insulation is required. This is the reason HT motors always wound in star connection."

http://www.allinterview.com/showanswers/85678.html

http://powertips-elec.blogspot.com/2010/12/motor-starting-schemes.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3
In reply to #2

Re: HT motors

06/08/2012 5:02 AM

I don't follow "HT motors operate on high voltage ( 6.6 or 11KV). IF we make delta connections than voltage experienced by windings will be line voltage, which will require more insulation of winding. In star connection voltage experienced by each winding is phase voltage hence less insulation is required. This is the reason HT motors always wound in star connection." even if it is 32/0 in favour.

The insulation has to stand the voltage difference between the metal of the stator (effectively ground) and the volts in the winding. That voltage difference is line voltage/√3 whether the motor connection is star or delta. If that's wrong will somebody please explain why?

It may well be true that for some reason HT motors are always wound in star connection, I wouldn't know offhand.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: HT Motors

06/08/2012 2:10 PM

In the star connection the winding insulation must withstand the phase to ground voltage. In the delta the winding must withstand the phase to phase voltage.

The starting current for a high voltage motor is much less that an equivalent low voltage motor, thus much less line disturbance..

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #4

Re: HT Motors

06/08/2012 2:54 PM

I don't get that. The way I see it the voltage across the insulation is phase to ground in both cases. How does the "other" side of the insulation get to see the other phase voltage?

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #5

Re: HT Motors

06/08/2012 4:10 PM

I know what star and delta connections look like, but I don't think the diagrams help to determine the voltage across the insulation, which is what we're discussing. If you could connect a voltmeter between a point on the outside of the winding (under the insulation) and a point on the stator metal (which is at ground or neutral potential) in contact with the outside of the insulation, I think the reading would be same in both cases, 230 volt. That's at the end near the line connection, it might vary at different points along the winding, I haven't thought that through.

I didn't see anything on your link that referred to it.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: HT Motors

06/08/2012 5:00 PM

I thought we were talking about limiting start up current....This is from the previous link...

"It is, however, advisable to employ only HT motors, in large ratings. HT motors have little alternative to be switched other than a DOL or a soft starting. Y/D switching in an HT motor is neither advisable nor possible for its windings are normally wound in a star formation to reduce the winding's design voltage and economize on the cost of insulation. Auto transformer switching is possible, but not used, to avoid a condition of open transient during a changeover from one step to another and for economic reasons as noted above. Moreover, on a DOL in HT, the starting inrush current is not very high as a result of low full-load current. For example, a 300 hp LT motor having a rated full-load current (FLC) of 415 A on a DOL will have a starting inrush of approximately 2500 A, whereas a 3.3 kV motor will have an FLC of only 45 A and starting inrush on a DOL of only 275 A or so. An HT motor of 3.3, 6.6 or 11 kV will thus create no disturbance to the HT distribution network on DOL starting."

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #7

Re: HT Motors

06/08/2012 9:51 PM

Just to add an autotransformer configured, as a Korndorfer starter doesn't have an open transition.

The down side, they are still expensive.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#10
In reply to #7

Re: HT Motors

06/09/2012 9:38 AM

Giving whoever wrote that the benefit of the doubt and assuming he knows what he's talking about, fair enough, but I still don't see the logic of it.

I looked on a few websites for HV motors, and there wasn't much about star/delta connection. What there was did refer mostly to star, but delta was mentioned.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: HT Motors

06/09/2012 3:39 AM

Homework??

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#11

Re: HT Motors

06/11/2012 3:06 AM

You have not mentioned the size of the motor, nor the type of the equipment coupled with the motor. Normally HT motors can be started direct on line unless they are large size motors. If the inertia of the driven equipment is high, the starting current will persist for longer duration, otherwise the starting current will fall within a short time.

In case of assisted starting using reactor/ autotransformer or electronic soft starters, starting current and torque will be less but starting time will be more.

If the cause is ' limit starting current ' (for large motors) then effect will be ' long duration starting ' using assisted starting. If the cause is ' develop more starting torque ', which assisted starting will not be able to provide then effect will be ' high starting current but of shorter duration ' using DOL starting. You have to adopt the right method of starting depending upon the application.

Register to Reply
Register to Reply 11 comments
Copy to Clipboard

Users who posted comments:

brich (1); Codemaster (4); debata07 (1); nobodysomebody47 (1); SolarEagle (2); TonyS (1); wareagle (1)

Previous in Forum: Constant Percentage Impedence of Auto Transformer   Next in Forum: Why Motor Start Current (DOL start) is 4-7 Times of Its Rated Current?

Advertisement