Can anybody provide me Busbar sizing calculation sample copy with sld....It will be very helpful for me.
CR4 Admin: removed email address
Re: busbar sizing
06/29/2012 3:04 AM
Re: busbar sizing
06/29/2012 3:35 AM
Re: busbar sizing
06/29/2012 5:44 AM
Re: busbar sizing
06/29/2012 6:25 AM
Once you calculated full load current next select the conductor typetype(Al or Cu).If it is Al current density is 0.8A/mm2...If it is Cu current density is 1.2A/mm2...
Let us consider for 800A
the bus bar size is Full load current/(current density)...
for Al conductor...
bus bar size = 800/(0.8) =1000for standard 100x12 size....for Cu conductor
bus bar size = 800/(1.2) =666.66for standard 75x12 sizeCu conductor..
Re: Busbar Sizing
06/30/2012 5:54 AM
Actually i have 1 DG rated 40 KVA,415 V(+/-5%),0.8 PF.Now guyz plz show me bus bar calculation for the system.
Re: Busbar Sizing
07/01/2012 11:03 AM
Sure, you are an electrical engineer?
Exploring the Science of Electricity
Re: Busbar Sizing
07/03/2012 1:40 AM
harry im 2nd yr student.