Electrical Engineering: Circuit Design Questions

07/12/2012 1:10 AM

I have two questions about the circuit design:

1. Why are HV induction motors star connected which are different from delta connected windings in LV motors? As far as I know, motors with the same power can be smaller in delta connected than in star connected. So why is a star-connected HV motor preferred?

2. In HV circuit, the secondary of a Voltage Tx (110V) is always connected with the L2 (Yellow phase) to the ground (earthing point). So why is this so designed rather than connecting the star point to the ground?

Thx for enlightening me.

Clement

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#1

Re: Electrical Engineering: Circuit Design Questions

07/12/2012 11:35 PM

The question make no sense at all. HV / LV? 13kV, 450V, 110Vor 5V?

Mixing up star center neutral return with protective ground?

Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#2

Re: Electrical Engineering: Circuit Design Questions

07/13/2012 12:45 AM

QUIT before you injure yourself or someone else.

Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#3

Re: Electrical Engineering: Circuit Design Questions

07/13/2012 6:44 AM

I may be able to answer your first question, the second I have no idea what you are talking about.

Question 1:Most 3 phase motors are designed to be dual voltage;

Lets say 400 or 230 volts.

For a supply of 400 volt in this case we would wire the motor in star configuration, this is so that the windings are in series via connection at the star point

For a supply of 230 volt the windings are in parallel, no star point.

In this example the motor is delta connected at 230 volts, that means the windings are in directly wired across the phases. If you did the same at 400 volts you would have a motor burnout.

Best Regards

Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#4

Re: Electrical Engineering: Circuit Design Questions

07/16/2012 9:21 AM

1. HV motor is star connected so that voltage stress on the windings is reduced to root three times of line voltage; reducing the insulation cost and chances of failure due to less application of voltage.

2.In Secondary circuit of voltage transformer(110 volt) middle phase (L2/Y-Phase ) is earthed to facilitate to complete ground fault current path in case of occurence of ground fault in secondary circuit of voltage transformer and blowing off of protective HRC fuse (preferably 2Amp rating ) to save the secondary voltage circuit.

Manindra

__________________
Manindra
Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments