ETAP - Shunt Reactor Modelling

07/16/2012 6:17 AM

Please explain how to model shunt reactor in ETAP. Even we used static load method and it is also not showing proper result.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: ETAP - Shunt Reactor Modelling

07/16/2012 9:10 AM

What result were you expecting and what result did you get? Where are they located, more detail will get better answers.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#2

Re: ETAP - Shunt Reactor Modelling

07/19/2012 7:02 PM

If I understand correctly that shunt reactor is used in large power transmission by high voltage under ground cable in city areas. Large size of cable draws large amount charging current from source. The large charging current of the cable is balanced by full load (kVA) lagging power factor at receiving end. If load is small or lean at any time of the 24Hr, then balance of charging current will be affected and the load end of the cable terminal voltage will rise more than the insulator bearing capacity (some times called as Ferranti Effect). Owing to increase of terminal voltage in lean load at terminal, there might be break down of terminal insulators' insulation. To avoid this condition, a fixed or Thyristor (SCR) controlled variable shunt Reactor is connected at the load receiving end of the cable terminal.

Modeling of the Shunt Reactor for program will be done as first estimate preliminary shunt Reactor impedance value in Ohm. This impedance will be divided by the Base impedance at that cable end voltage system. Shunt Reactor will now be in Per Unit. This per unit shunt reactor one end is connected to the cable terminal Bus and other end will be grounded. This Model will be used in any Load Flow program such as IPSA-UK or ETAP-USA to study Power System Analysis.

__________________
B.E, M.I.E, M.S
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#3
In reply to #2

Re: ETAP - Shunt Reactor Modelling

07/31/2012 9:23 AM

With all do respect, you did not answer the question, the question was "how to model reactors in ETAP".. a software was already specified.

@kanmano

You can also use Lump Load for reactors. Just make sure you know about your reactor. And make sure you use the constant z = 100% and enter the appropriate value for the KVAR, single phase/three phase.. reactors are modelled as constant z in etap.

Register to Reply
Active Contributor

Join Date: May 2010
Posts: 10
#4
In reply to #3

Re: ETAP - Shunt Reactor Modelling

08/03/2012 7:53 AM

Thanks hkian. We tried with lump load method. say if I consider 200kVA as lump load for reactor its drawing 200kVA from the source. Where as in the actual condition it should not draw any power otherthan the losses which is likely around 5% of the value.

Register to Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#5
In reply to #4

Re: ETAP - Shunt Reactor Modelling

08/09/2012 9:05 PM

Just like i said, it is modelled in constant z. Let's use your example, the 200kVA reactor, you said that it is drawing 200kVA from the source. Now, for me, in my opinion, you are using the voltage that is different from the actual reading.

in constant impedance models, kva = (voltage^2)/impedance, right? so the power being drawn by the reactor is dependent on the voltage of the system.

please do check if the voltage is the same in the actual readings. or, please model the shut reactor a constant z, whereby you will input the impedance.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hkian (2); kanmano (1); Mushtaq Hussainh (1); RAMConsult (1)