we have a network of 6.6KV distribution system fed from 132 KV grid station through a 132/6.6KV power transformer.the 6.6KV bus has an undervoltage relay whose setting is 85% of 6.6kv i.e U/V setting =5.61KV. 
the transformer tap changer does regulation of 6.6KV secondary voltage between 118KV and 145KV primary grid voltage ( i.e. between taps 1 to 27).below 118KV on the primary side of transformer, the secondary 6.6KV side voltage decreases linearly according to the V1/V2=N1/N2. relation. now according to the 85% setting of 5.61KV on our 6.6KV bus under voltage relay, the primary voltage should be 112KV i.e. 85% of 132 KV. but we have seen that even if the primary voltage falls as low as 103KV , no tripping of the 6.6KV bus load feeders and incoming feeder occurs which is very strange. v have checked our under voltage relays and replaced them but no problem is found with them. i do not know the justification of no bus tripping below 112KV on primary side of transformer to provide.
help needed please.