Hi,
Is there a governing ASHRAE standard or any specific design criteria to be followed during design of a radiant cooling system?
The ambient conditions are DB 43Deg C/70% RH. Desired indoor temperature is 24Deg C.
Chilled water is available at 16Deg C.
Thanks
Harish
Pathfinder Tags: ASHRAE HVAC Radiant Cooling
Re: ASHRAE standard for Radiant Cooling
07/28/2012 1:26 PM
ASHRAE 1996, page 6.1.2)
Re: ASHRAE Standard for Radiant Cooling
07/29/2012 3:00 AM
ASHRAE Handbook. HVAC Systems and Equipment 2008. Chapter 12. Hydronic Heating and Cooling System Design.
ASHRAE Handbook. HVAC Systems and Equipment. Chapter 6. Panel Heating and Cooling Design. ASHRAE. 2008.
You can also refer CIBSE ( U.K ) guides.
07/29/2012 4:06 AM
Thank you!