Anonymous Poster #1

What % Allowed Neutral Current

08/06/2012 2:37 AM

Dear sir

we have 3 PHASE un balanced loads in our iidustry , we conwsume load ampps 1000A, 850A. 900 A in R phase. Y and B phase respectivily and 80-95 A in NE.

so please kindly clarify NE current Range.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#1

Re: what % allowed Neutral current.

08/06/2012 3:28 AM

Unless your loads are very specific i.e. lots of large motors I would suggest at least a full size neutral if not greater. Worst case is you fully load one phase in which case all of the current would come back through neutral.

If your loads are fixed 3phase then you could reduce the neutral.

It may be you have issues with harmonics in which case you might not need to increase the size of the neutral above that of the phase.

Schneider have a paper on a transformer overloaded by harmonics.

You are the engineer - you know the load you are connecting - we don't.

Reply Good Answer (Score 2)