Electro Pneumatic Positoiner EPL Type

08/07/2012 5:34 AM

Hi

The currently I'm using some instrument equipments, and now some control valve " Electro pneumatic positioner EPL type" met trouble as below:

Normally the controller working with range (4~20mA DC) same (0~100% opening valve).However recently some of them met trouble that when we input 12mA the controller open 100% of valve and keep therer but as the theory it must open 50% of valve, then we change input pressure it work normally in some hours and then it met trouble again.

I saw manual but i don't have any information about that trouble

Please support me if you know

Thanks

CR4 ADMIN - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#1

Re: Electro Pneumatic Positoiner EPL Type

08/07/2012 11:10 AM

In the event of loss of electrical or pneumatic input signal, positioners are designed to have its output go to fail-safe position.

I wonder if the move to 100% is a fail-safe response to loss of input signal.

Reply
Participant

Join Date: Aug 2012
Posts: 1
#2
In reply to #1

Re: Electro Pneumatic Positoiner EPL Type

08/08/2012 2:04 AM

Hi

Please kindly see the my report for the testing the pneumatic input signal and the position of the positioner

Output signal from DCS to Valve ( disconnect DCS output signal cable at positioner (Bzone top A only))

Butterfly valve B zone top A

BV 5201
MV(%) openning of valve(%)
0%3.908mA
50%12mA
100%20.998mA

Connect DC signal source/ Output 4-20mA (B zone top A only)

Butterfly valve B zone top A

BV 5201
4-20mA openning of valve(%)
40%
1250%
20100%

However, sometime it met trouble is alway 100% positino although we try to set down

it is not a fail-safety response to loss input signal because when it is met trouble we check mA is Ok( same output from DCS)

Reply Off Topic (Score 5)
Member

Join Date: Oct 2010
Location: Central Oklahoma, USA
Posts: 8
#3

Re: Electro Pneumatic Positoiner EPL Type

08/08/2012 10:57 AM

We had a similar problem with a Sullivan & Sons Valve Positioner.

Make sure the unit has a good ground connection and ground the shield of the 4-20 mA signal at the positioner. (The shield by itself does not provide a good ground to the unit.)

vM

__________________
"If you can't explain it simply, you don't understand it well enough." (AE)