Transformer Testing

08/13/2012 4:16 AM

what is the difference between high voltage test and tan delta test in transformer.

please explain.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#1

Re: transformer testing

08/13/2012 5:41 AM

you see high voltage test and tan. delta test?

one thing as very little to do one to another!

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Transformer Testing

08/14/2012 6:35 AM

An induced voltage (high voltage??) test proves that the transfo does not have any insulation breakdown at several times rated voltage (usually applied to the low voltage winding, between its terminals). Because any normal transfo will saturate at 120% rated, or so, voltage test has to be done at a proportionally increased frequency e.g. 150 Hz at 3 x rated volts for a 50 Hz transfo, using a special test generator.

You can do an isolation test between windings at rated frequency or DC, this would usually be described as an insulation test

"Tan Delta" usually refers to the loss angle of a capacitor. In the case of a transfo, the loss angle of the insulation between one winding and the others (which are earthed, also the core) is measured. A high loss indicates poor condition of solid insulation or oil.