Line Losses Percentage

08/28/2012 11:44 AM

We have got three transformers in our industry capacity 2000kva,1000kva & 400 kva .one meter is installed at the HT room where the supply is coming from the electricity board.We have installed sevral energy meters at various sections. but the problem is that the electricity board meter is showing reading 11% more than our internal energy meters.So is there 11% line loss there. how much is the valid line loss If its higher how can i reduced it. pls suggest.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: line losses %age.

08/28/2012 11:57 AM

Depending on the quality of the three transformers they could be responsible for most of your losses right there.

Add in that most power meters running through VT and CT's can have a +- 2 - 5% variance between them and that could be your sources for the discrepancy right there.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Line Losses Percentage

08/28/2012 8:12 PM
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Line Losses Percentage

08/29/2012 12:13 AM

Your plant may be riddled with loose joints, dodgy splices, undocumented taps and grossly undersized cabling for all we know.

Is the cabling warm to touch? Is there a persistent aroma of burnt bakelite and plastic? Do your connectors glow?......

Start looking and probing. Repeat your consumption monitoring starting closer to the MDB and do some accounting as you work your way towards the loads. Tabulate voltage and current and cable size/length values as you go. You will find the energy leaks. You won't be happy.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 20
#5
In reply to #3

Re: Line Losses Percentage

08/29/2012 12:17 PM

our cable sizing, connection , thimbling are ok. i want to know valid %age of line losses.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Line Losses Percentage

08/29/2012 9:35 AM

I strongly suspect the accuracy of the CTs & VTs as well as that of the meters. Pl. send them for calibration. Also, it is advisable to have all the CTs/VTs/meters of same accuracy class to get identical readings.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: Line Losses Percentage

08/29/2012 10:02 PM
__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ashutosh goyal (1); electricalexpert65 (1); tcmtech (1); Wal (2); wareagle (1)

Previous in Forum: Ultracapacitor to Recharge My Laptop?   Next in Forum: Ceiling Fan Speed

Advertisement