Anonymous Poster #1

Electrical Question

08/31/2012 2:35 PM

What is the difference between tpn mccb and 4 pole mccb? Why do we use tpn instead of 4 pole mccb?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Electrical Question

08/31/2012 3:05 PM

All 4 contacts break at the same time in a 4 pole MCCB. In a TP+N neutral breaks just after the phase contacts.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Electrical Question

08/31/2012 3:55 PM

TPN will mean triple pole with Neutral. TPN will mean a 4Pole device with 4th Pole as Neutral. 4 pole mccb has 4 poles. Basically both look same, except the current carrying capacity of neutral pole is less than the other poles.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Electrical Question

09/01/2012 12:09 AM

Go through the recent threads,you will find the answer.

__________________
pnaban
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Electrical Question

09/02/2012 3:12 AM

In TPN (three pole + neutral) breakers, only three phase poles would have the releases (thermal & magnetic) and the fourth neutral pole is only a switch without any releases in it. Whereas in four pole breakers, all the four poles would have releases. But, this is more a feature in MCBs only and NOT in MCCBs. In MCCBs you either have three pole or four pole. TPN MCCBs are unheard of as a product. May be, a three pole MCCB with external isolable neutral is called a TPN MCCB is tender specifications.

The choice of Three Pole MCCB + Isolabe Neutrla over a four Pole MCCB is economical, as the first arrangement is chaeper than the second.

Hope it is clear.

Reply