Turning Vanes

09/07/2012 12:14 PM

ARE TURNING VANES NECESSARY IN 45 DEGREE ELBOWS? THEY ARE KILLING ME ON TIME. I WOULD LIKE TO QUIT USING THEM BUT NEED SOME AMMO FOR MY REASON FOR ELIMINATING THESE VANES.

I AM ALSO INSTALLING VANES IN LOW PRESSURE DUCT WHERE THE FLOW IS BELOW 1000' PER MIN. CAN THESE BE DONE AWAY WITH?

THANK YOU, MIKE

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Piping Design Engineering - Retired Piper

Join Date: Feb 2007
Location: Bayonet Point, Florida
Posts: 635
Good Answers: 61
#1

Re: SHOP GUY

09/07/2012 12:57 PM

You need to give a little more information if you want help here.

Such as:

  • The size of these 45 degree elbows.
  • Are they really Elbows (as in Pipe) or are they Bends (as in Duct work)?
  • If they are Elbows in pipe what is the commodity?
  • If they are Elbows in pipe why do you think you need "turning vanes"?
__________________
Do it once and do it right
Register to Reply
Active Contributor

Join Date: Sep 2012
Posts: 12
#2
In reply to #1

Re: SHOP GUY

09/07/2012 1:13 PM

THESE ARE BENDS AS IN DUCT WORK. THE SIZE VARRIES. RIGHT NOW I AM IN THE PROCESS OF BUILDING 20"X18" 45 DEGREE BENDS. THE CHEEKS WILL BE THE 18" SIZE.THESE ARE USED FOR MOVING CONDITIONED AIR .

THANK YOU,MIKE

Register to Reply
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Turning Vanes

09/07/2012 2:53 PM

Turning vanes increase the efficiency of the ducting system. If you remove them, the characteristics of the airflow will change and the system may not have adequate pressure.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#4

Re: Turning Vanes

09/07/2012 11:36 PM

Any time turning vanes are used they CREATE a certain amount of pressure drop. The "trick" is to use them so that their drop is less than would occur if they were not in place.

The big issue comes from the INERTIA of the moving air. It WANTS to keep going straight, curved elbows create a gradual force to keep pushing the air around the ell but square throat ells will let the air "impact" the outside wall and then build up a pressure pocket which will push on the other side of the ELL and the be pushed out the opposite side opening- triggering lots of pressure drop and eddying of airflow which triggers lots of sound. The turning vanes slice into sections of the air and create small radius elbow effects (with some pressure drop) but relatively quiet and smooth airflow to the next duct section.

They are NORMALLY used to allow the installer to use a compact elbow- less metal and smaller size- rather than a correctly sized full radius elbow. The only OTHER time they have value is if the outlet is VERY close to the elbow, so that the air does not get pushed to the outer side of the ell, causing eddying and inconsistent airflow at the outlet.

Generally, 45 ells do not create enough loss or "pooling" of the air flow enough to cause a problem and they are almost never near an outlet. The slight amount of inertial pooling is quickly dissipated by the straight duct following the elbow.

Another option- about the same area but less air disruption and resulting drop- would be to transition to a wide, shallow duct elbow which would mimic the turn vanes but in a whole duct sort of way. However, the cost of the transitions, making the wide elbow, and installing same would likely be higher than the turn vanes. However, I really do not believe the is a need for turn vanes in 45 ELLs. especially a low velocity duct.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#5

Re: Turning Vanes

09/07/2012 11:42 PM

Please turn off your caps lock key! ALL CAPS is considered shouting, and you don't need to shout for us to 'hear'.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Commentator

Join Date: Aug 2010
Location: VA
Posts: 84
Good Answers: 4
#6

Re: Turning Vanes

09/08/2012 9:15 AM

Why would you use turning vanes unless directed to. What authority is requesting them?? At 1000'/min. is seems odd for low pressure duct to do so without specific requirements. Residential ducts dont have them unless your looking at a 1950's design. The cost and benefit are not there unless something really big is being designed. Also what are the duct dimensions? Again why would you do this effort without the customer specs. requiring it, specifically? Woody

__________________
Life is short, eat your dessert first .......In theory there is no difference between theory and practice. In practice there is. Yogi Berra
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#7

Re: Turning Vanes

09/10/2012 4:59 PM

At that velocity and with 45 instead of 90 elbows I think turning vanes would be gililding lilies. A check of pressure drop charts would help you make the decision.

Lou Bindner

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dkwarner (1); energygod (1); Lou Bindner (1); PennPiper (1); RICHARDMICHAEL (1); waldig (1); WJMFIRE (1)

Previous in Forum: Rate Of Flow From A Tank For A Given Pressure Drop?   Next in Forum: Iced Evaporator

Advertisement