Motor Winding Resistance

09/20/2012 2:51 AM

Can the equivalent winding resistance (ph-ph) of a 3 ph motor (160KW) be balanced even though there is a winding turn fault? This happened in one of the motors at our plant. There was small difference in inductance value though.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Motor winding resistance

09/20/2012 3:00 AM

"there is a winding turn fault"

Please give full & complete detail about winding turn fault. What are the Amps drawn by each phase?

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#2
In reply to #1

Re: Motor winding resistance

09/20/2012 3:18 AM

Pls clarify more.Aftr disconnecting the delta connection,the problem was found out.But in delta connection,the values must have been unbalanced isn't it? For small winding turn faults,will there be not any change in equivalent resistance of the all 3 phase.?

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3
In reply to #2

Re: Motor winding resistance

09/20/2012 4:21 AM

Unless you can measure at milliohms level! What led you to measure resistance in the first place. What observation of yours started this hunt?

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#4
In reply to #3

Re: Motor winding resistance

09/20/2012 4:40 AM

The motor tripped on unbalance during running.So as usual we checked the winding resistance (ph-ph)without seperating the windings at motor TB.Took trial & motor tripped again during starting itself. My question is doesn't the inter turn shorts make the resistance unbalance,but sufficient for the protection relay to trip the motors.?

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#5
In reply to #3

Re: Motor winding resistance

09/20/2012 4:47 AM

The motor tripped on unbalance during running.The winding resistacne was found 0.2ohm.When it tripped again on starting,we found the 2 of the winding short after seperating the motor cables.My question is,why this fault didnt reflect on the meter.Whether micro ohmmeter is being used everwhere for motor winding resistance & we should also employ that method.?

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#6
In reply to #5

Re: Motor winding resistance

09/20/2012 5:24 AM

When measurement levels are in decimal, it is obvious what kind of instruments should be used. This is my commonsense postulation. I am not aware, what everybody uses, under such circumstances. Somebody, sooner or latter, will tell us about that.

"why this fault didn't reflect on the meter"

Because earlier you did not isolate the motor cables before taking measurement. Or there might have been a slip-up somewhere. It is a thought. I am not accusing anybody of anything.

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#7
In reply to #5

Re: Motor winding resistance

09/20/2012 8:22 AM

Due to the low resistance values you are reading, yes, you should use a micro-ohmeter, but even this won't reveal significant unbalances, for that you should perform a surge test, it will alert on minute turns count diferences between windings, insulations integrity and turn to turn shortings, even at the scale of one single turn.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8

Re: Motor Winding Resistance

09/21/2012 12:31 AM

lead resistance is normally done with DC. For a single shorted coil with say 100 turns will give only a 1% change. When the coil is excited with AC the shorted turn now appears as a short to the AC flux change. That is the principal of flux linkage. That shorted turn will give a high current for the AC.

I had a DC machine, 500kw, 500vdc, short a turn in the shunt field. Now you would expect that a dc coil fed with DC would not have any problems. But the DC supply was an unfiltered phase controlled bridge. At the rising edges of the waveform a very high current flowed and opened the SCR protective fusing. The root cause of the failure was a partially blocked cooling duct - the motor over heated, but the klixon was installed at the inlet and not the outlet. The winding failed on the "hot" end.

Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#9

Re: Motor Winding Resistance

09/21/2012 12:40 AM

Motor faults can occur from the winding heating up. The thermal expansion will then cause a short, but when it cools, the windings return to their normal position and show no signs of shorting.

A good way to test motor problems is to run an ammeter (three if three phase). Remember that measuring the resistance of windings can only be done when the motor is not energized, hence a static condition. Also, if a few windings are shorted, a meter may not read the difference in resistance. The resistance of the winding is based on length of wire and resistance of the wire material (micro or milli ohms per foot). You can see how a small short (10-20 windings) will not have much effect on the resistance, but measuring current or impedence will show the short.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#10
In reply to #9

Re: Motor Winding Resistance

09/21/2012 3:02 AM

Thanks a lot to all......by the way can anybody tell what's the nromal range of resistance & inductance of any rated induction motors.This would help veryeasily.

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#14
In reply to #10

Re: Motor Winding Resistance

09/27/2012 8:39 AM

Dear giri,

Best way to check this type of fault by using Electirc Motor Checker instrument. In case of inter turn fault, when you measure % inductance,(R-N,Y-N, B-N,if neutral point is accessible, otherwise,R-Y,Y-B,B-R,),there will be variation of the readings. Normally,if the readings are differing more than 3to 5%, it indicates there is a interturn fault.

Manindra

__________________
Manindra
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#11

Re: Motor Winding Resistance

09/21/2012 9:40 AM

Resistance of winding for 127 kW motor 460 V Delta 60Hz 4 pole

  • colt motor, at 27.2 °C winding, frame and room temperature
  • U1-U2 : 0.02174 Ohm
  • V1-V2 : 0.02168 Ohm
  • W1-W2 : 0.02169 Ohm
  • warm motor, at 96.4 °C winding, 74.5 °C frame, 32.2 °C room temperature
  • U1-U2 : 0.02790 Ohm
  • V1-V2 : 0.02776 Ohm
  • W1-W2 : 0.02787 Ohm

These values come from a type test of a 127 kW motor.

For a 160 kW motor the values will be smaller.

Values depend on pole number, voltage, motor construction

  • more poles, higher resistance
  • higher voltage, higher resistance

Because the values are very small, it is difficult to measure them.

The resistance measurement will be affected by difference in length of connection cables,

  • difference in torque of connection bolts
  • difference in material from cable shoes, washers, Cu bolts, Fe bolts; etc
  • difference in material from test clips micro ohm meter

Almost impossible to make a correct measurement

Register to Reply
2
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#12

Re: Motor Winding Resistance

09/21/2012 10:18 AM

Partial shorts in a coil winding is not easily detectable through an ohm meter. Meter sensitivity and meter internal resistance will interfere your meter readings. To diagnose partial winding shorts, a high frequency inductance meter will be a more effective tool to use. It will show even by just using inductance comparison the winding inductance, differences between good and questionable phases.. I had effectively use this tool in my past dealings while working with any type of coils, be it transformers, motors, etc.

Good luck...

__________________
vsar
Register to Reply Good Answer (Score 2)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#13

Re: Motor Winding Resistance

09/21/2012 2:33 PM

Have you tried to do a insulation test using a mega-ohm meter when the the motor is cold and when it tripped? The windings should be totally isolated from the supply and from each other.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Autobroker (1); giri (4); GW (1); Icarus (1); Joshi (3); manindra (1); rudy.leurs (1); vsar (1); Yahlasit (1)

Previous in Forum: How Does a Synchronous Condenser Start Up?   Next in Forum: Solar PV System

Advertisement