we have auto transformer 400/132/11kv the tertiary winding (11kv) delta connected and this delta connected earthed across 21hom resistance . the question Is it permissible to earthed delta winding across the grounding resistance only with out zigzag transformer? but passes current in this case? But is that a short circuit?

Thanks for all.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Earthing of delta winding

09/29/2012 2:37 AM

I believe, the answer is some where around HERE

Register to Reply Score 1 for Off Topic
Anonymous Poster #1
#2
In reply to #1

Re: Earthing of delta winding

09/29/2012 2:30 PM

This practice of providing a ground on the DELTA winding is common on STAR-STAR Power transformers. The purpose of grounding the OPEN DELTA winding is to stabilize the SECONDARY VOLTAGES of the Power Transformer under normal conditions.

Another reason for gronding the OPEN DELTA winding is to prevent the FLOW OF ZERO SEQUENCE currents through the transformer under fault conditions.

Register to Reply
Commentator

Join Date: Sep 2012
Posts: 58
#3
In reply to #2

Re: Earthing of delta winding

09/29/2012 4:48 PM

please Mr. Anonymous

what do you main by OPEN DELTA winding .the Tertiary winding (delta winding) in our auto transformer not open .

Register to Reply
Active Contributor

Join Date: Sep 2012
Posts: 12
#4
In reply to #3

Re: Earthing of delta winding

09/30/2012 7:28 AM

The tertiary(11kv) winding is called OPEN DELTA because there the 11kv is not feeding any external load. The winding is so designed that the net magnetic balance on it is zero(hence net voltage is also zero). Hence a resistor can be connected across it without any net current flowing at normal system conditions.

However, when an external Earth Fault occurs, the resulting zero sequence currents set up flow through this OPEN DELTA winding to ground.This prevents the zero sequence currents from flowing through the Transformer. This also prevents abnormal DIFFERENTIAL RELAY operation of the Transformer for external faults.

2. Grounding transformers(zigzag-star connected) are used to provide paths for zero sequence currents on delta connected circuits.

At the moment I had no means of sending you a DIAGRAM of how the connections look like. However, the NAMEPLATE DATA on the Transformer at times shows the connection of how the OPEN DELTA looks like.

Please check the nameplate data of your transformer.

Regards

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2012
Posts: 58
#6
In reply to #4

Re: Earthing of delta winding

10/01/2012 11:49 AM

Dear sir

Thank you very much to answer, but why not consider connection OPEN DELTA by resistance to earth short-circuit

thanks for all

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #3

Re: Earthing of delta winding

09/30/2012 8:41 AM

Please visit www.i-gard.com and they have the answers to your questions in their technical publications.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); FADHEL (2); Joshi (1); Olu Gyibrilla (1)

Previous in Forum: Pressure Test on Transformer   Next in Forum: Modifying a 1.2 GHz Receiver to Pick Up 1.3 GHz

Advertisement