Blowing of 200 Amp D.O.Fuse (33KV)

10/03/2012 1:23 PM

Sir, we are 33KV HT consumer,contract demand is 4000 KVA, actual load vary from 3200kw to 3600 kw X'mer 2500 KVA(4 Nos). It is a shopping mall. Our problem is that the DO fuse is blown, previously we used 150 Amp DO fuse,now it is 200 Amp rating. Our protection system is OK.

pl.give me solution of this problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: blowing of 200 Amp D.O.fuse (33KV)

10/03/2012 1:44 PM

"our protectionsystem is ok." It doesn't sound like it to me.

Why were the fuses uprated? Is affecting just one transformer?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Blowing of 200 Amp D.O.Fuse (33KV)

10/03/2012 11:21 PM

Could be something as simple as excessive inrush current or an incorrectly sized fuse (current or tripping curve or both.

Do you have lots of air conditioning that is set to turn on at the same time?

__________________
jack of all trades
Register to Reply
Associate

Join Date: Feb 2010
Posts: 35
#3

Re: Blowing of 200 Amp D.O.Fuse (33KV)

10/04/2012 10:07 AM

Hire a qualified engineer before someone guesses what the problem is, fails, and causes a calamity which hurts or kills a lot pf people.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Blowing of 200 Amp D.O.Fuse (33KV)

10/04/2012 5:03 PM

You are saying that you have 4 x 2500 kVA transformers ==> 10 MVA which requires a 175A fuse to supply the 4 transformers.

If your demand is 3200 to 3600 kVA, is it from the 4 transformers or just from 2 units and the rest is supplying some other sections?

4000 kVA means 3200 kW and 2 trans will be 5000 kVA == 4000 kW (70A max)

To Blow the 150 A fuse, there must be other loads or a significant surge, OR there is a faulty connection somwhere. High Tension (33 KV) is delicate on junctions being properly done and professionally done. It is easy to make a slopy connection with bad insulation that can leak to ground.

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#5

Re: Blowing of 200 Amp D.O.Fuse (33KV)

10/04/2012 8:01 PM

If you know your load has not increased, De-energize the system and check the corona shields for failure at the terminations and inspect your surge arrestors for fault(s) if equipped.

If there is not any visible damage, make sure all loads and surge arrestors are disconnected then perform a meggar, hypot, or AC HV test of the system.

If no faults are identified, re-energize the system with all loads disconnected then allowing a significant amount of time between closures, energize each load one at a time until the fuse opens/blows.

Whichever load opens/blows the fuse then must be analyzed/tested to locate the fault.

Register to Reply