Isolation Transformer

10/14/2012 3:16 AM

Hi

Can anybody tell me that what is the per phase current of 3 phase, 200KVA Isolation Transformer?

Register to Reply
Pathfinder Tags: isolation transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: ISOLATION TRANSFORMER

10/14/2012 6:06 AM

No, not without a voltage.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#2
In reply to #1

Re: ISOLATION TRANSFORMER

10/14/2012 6:17 AM

3 phase voltage is 415 volt line to line

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: ISOLATION TRANSFORMER

10/14/2012 7:30 AM

278.2A

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Isolation Transformer

10/15/2012 5:12 PM

Muhammad Salman

What is your position?
Are you an engineer?

Register to Reply
Anonymous Poster #1
#5
In reply to #4

Re: Isolation Transformer

10/16/2012 12:00 AM

Hi

If you dont mind can you share the calculation how you got the answer as 276.4A,What is the power factor you have taken,what the formula you have used

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#6

Re: Isolation Transformer

10/16/2012 3:16 AM

The 278A was right. Where did 276A come from? Power factor????

Register to Reply
Anonymous Poster #1
#7
In reply to #6

Re: Isolation Transformer

10/16/2012 12:30 PM

Its 278 A typing mistake

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#8
In reply to #7

Re: Isolation Transformer

10/16/2012 12:40 PM

line current

200 000 / 415 / 1.732

where 1.732 is square root of 3.

ans - 278.25A

Register to Reply
Anonymous Poster #1
#9
In reply to #8

Re: Isolation Transformer

10/16/2012 11:47 PM

Thanks for the reply , Is there any isolation transformer which is having power factor more than .8. If so what are they , What are the moderntype of transformer where to reduce traditional loses

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#10

Re: Isolation Transformer

10/17/2012 3:39 AM

Don't you determine the pF by your connected load? Put a resistive load on and you can forget about pF. With a load of lossy motors and inductive lighting .......

On a decent transformer losses will be minimal.

Suggest you get a senior electrical guy on board to check what you are doing.

Register to Reply